Just to clarify regarding part load. Latent loads are not neglected, but the
PLR is calculated based on the sensible portion of the load delivered divided
by full-load sensible capacity.
Mike
On 24 Mar 2005, at 13:15, Richard Raustad wrote:
>
> See comments below:
>
> deserteagle_zhou wrote:
>
> >
> > Hi,all,
> > I have two questions about the DX Coil Model .
> > 1.For the DX Coil Model -- DX Cooling Coil Model, there is a
> > sentence in the EngineeringDoc.Doc ,¡°The total cooling capacity
> > modifier curve (function of flow fraction) is a quadratic curve with
> > the independent variable being the ratio of the actual air flow rate
> > across the cooling coil to the rated air flow rate (i.e., fraction
> > of full load flow).¡± The ¡° the actual air flow rate across the
> > cooling coil¡± seems to be a mean value in a timestep.What does that
> > mean exactly?
>
> You are correct, the air flow rate reported by EnergyPlus is an
> "average" value for the
> simulation time step when the DX system's fan cycles on and off to meet
> the sensible cooling load.
> This average value is determined by the air flow rate across the cooling
> coil when the fan is on
> multiplied by the fraction of the time step the fan operated. So the
> "actual air flow rate across the
> cooling coil" referred to above means the air flow rate when the fan was
> on, NOT the average
> reported each time step.
>
> > How can I define the "the actual air flow rate
> > " from the manufacture's catalogue data in order to get the
> > modifier coeficient?
>
> Manufacturers provide a rating for air conditioning systems at some
> nominal air
> flow rate and some "rated" inlet air condition. At this nominal air flow
> rate and "rated" inlet air
> condition, the manufacturer states a gross and/or net cooling capacity.
> Be careful to use the
> gross cooling capacity as stated by the manufacturer. If the
> manufacturer only provides a net
> cooling capacity, the fan heat must be subtracted to yield a gross
> cooling capacity
> (gross cooling capacity is higher than net cooling capacity).
>
> For this example, lets say its 1000 W gross cooling capacity at 2 m3/s
> nominal air flow rate and
> at a "rated" inlet air condition of 26.7 C dry-bulb and 19.4 C wet-bulb
> when the outdoor temperature
> is 35 C.
>
> The manufacturer also provides performance data tables at air flow rates
> different from the nominal
> air flow rate. Find the "rated" cooling capacity in the chart and note
> the "rated" inlet air conditions.
>
> So at indoor conditions of 26.7 C dry-bulb / 19.4 C wet-bulb and 35 C
> outdoor temperature we have
> from the performance data table:
>
> Air flow (m3/s) Capacity (W)
> 2.0 1000 *** rating point ***
> 1.5 850
> 1.0 657
>
> Next this data has to be normalized to 1 at the rating point as follows:
>
> Divide the air flow column by the rated air flow (2.0 in this example) and
> the capacity column by the rated capacity (1000 W in this example). Since
> capacity is a quadratic function of air flow I will also show the air
> flow rate squared in the example below. You get:
>
> Normalized Capacity Normalized Air Flow Normalized Air Flow squared
> 1.0 1.0 1.0
> 0.85 0.75 0.5625
> 0.675 0.5 0.25
>
> This normalized data set must then be curve fit according to the equation:
>
> Normalized Capacity = A1 + B1*Normalized Air Flow + C1 * Normalized Air
> Flow * Normalized Air Flow
> --- OR ---
> Noralized Capacity = A1 + B1*Normalized Air Flow + C1 * Normalized Air
> Flow squared
>
> When this is completed you will have calculated the regression
> correlation (I used a familiar spreadsheet) coefficients
> for Normalized Cooling Capacity as a function of air flow ratio (ratio
> of actual air flow to rated air flow) as:
>
> A1 = 0.25
> B1 = 0.95
> C1 = -0.20
>
> The EnergyPlus curve object would then look like this:
>
> CURVE:QUADRATIC,
> CapacityAsAFuncitonOfFlow, !- Name
> 0.25, !- Coeff1 Constant
> 0.95, !- Coeff2 x
> -0.20, !- Coeff3 x**2
> 0.0, !- minimum value of x
> 1.0; !- maximum value of x
>
> >
> > 2. From the formula of PLR, what do "sensible cooling load and
> > steady state sensible cooling capacity" mean respectively? How does
> > the program calculate them(Is latent cooling load neglected)?
> > Any suggestion and guide will be appreciated.Thank you in advance.
>
> The sensible cooling load is the load to be delivered by the AC system
> to meet the thermostat
> set point temperature. The sensible cooling capacity is is the capacity
> of the AC unit when it
> runs continuously. So if the cooling load is 100 W and the sensible
> cooling capacity is 200 W,
> then the PLR is 0.5 and the AC unit only runs 50% of the time.
>
> >
> > Eric
> >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files area of the Support Web Site.
> >
> >
> >
> > Yahoo! Groups Sponsor
> > ADVERTISEMENT
> > <http://us.ard.yahoo.com/SIG=129bec5qj/M=298184.6191685.7192823.3001176/D=grou
> > ps/S=1705007389:HM/EXP=1111718323/A=2593423/R=0/SIG=11el9gslf/*http://www.netf
> > lix.com/Default?mqso=60190075>
> >
> >
> >
> > ------------------------------------------------------------------------
> > Yahoo! Groups Links
> >
> > * To visit your group on the web, go to:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > * To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
> > be>
> >
> > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > Service <http://docs.yahoo.com/info/terms/>.
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/