Re: [EnergyPlus_Support] Other Error




1.  Have you autosized the controller convergence tolerance?

2.  Does the HVAC system draw completely (svg output file)?  If not, there is 
probably a node connection error somewhere.

3.  The "no valid range" warning indicates that the demand on the chilled water 
loop exceeds the highest load range specified in the Load Range Based Operation 
Scheme named "CHILLER:ELECTRIC".  Check the load ranges and increase the limit 
on the highest one to be something greater than 330753.


On 28 Mar 2005, at 0:29, energypluser wrote:

> 
> 
> Dear all:
> 
>       When I used the original data from a manufacture to simulate the 
> electric chiller, I got a problem here. The iteration exceeded to 100, 
> and another warning came out: 
>         Warning: No valid range found for Loop Demand=-330753.38 in 
> Load Range Based Operation Scheme=CHILLER:ELECTRIC
> 
>        How can I settle it down?
>        What does that warning mean ?]
> 
> Thank you in advance.
> 
>                                         Charlie
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/