Re: [EnergyPlus_Support] Electricity Error




This could mean the chiller is not operating at all during those months, or it 
could be a mistake in the reporting inputs.  First, turn on report variable 
"Chiller Evap Heat Trans Rate" to confirm if the chiller is operating.  If the 
chiller is operating, then check the reporting inputs and make sure there is 
not a schedule attached to the electiricity variable which may be supressing 
reporting during these months.   If the chiller is not running, check if there 
is a demand on the chilled water loop, "Plant Loop Cooling Demand".  Once you 
determine what is operating and what is not, you should be able to find which 
controls or schedules need fixing.

Mike


On 30 Mar 2005, at 6:28, energypluser wrote:

> 
> 
> Dear Mike,
> 
>      When I used the electric chiller as the cooling resources for a 
> entire year simulation, I get some warning about the humidity ratio 
> calculations. But I find that the electricity from April to September 
> do not output at all, and I can not calculate the Mean COP then.
> 
>      So what do you think is the cause for this situation?
>      Thank you in advance.
> 
>                                         charlie
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/