Re: [EnergyPlus_Support] convergence value
No. These convergence toleranaces in the BUILDING object are only used to
determine how many warmup days are simulated. The max/min zone temperatures and
zone loads are compared from one warmup day to the next. If they are within
these tolerances, then warmup is declared to be converged and the simulation
proceeds. If not, another warmup day is run. (Ref. Input Output Reference, p.
10, pdf p 40).
Zone thermostat controls have no tolerance or throttling range. If the heat
balance predicts that the zone temperature will fall below the heating setpoint
by any amount, then a heating load request is passed to the HVAC system.
Mike
On 10 Apr 2005, at 20:50, ogocer@xxxxxxxxxxxxxx wrote:
>
> Dear all,
> i want to check my information about convergence value in C degree or Watt. i
> understand it according to the following explanation, we set some setpoints in
> temperature or watt. for example heating setpoint is in c or shading setpoint is
> in watt. if i set heating setpoint 21 C degrees and my convergence tolerence
> value is 0.4 c degree. Then heating will also start at 20.6 C degree. "This
> value represents the number at which the loads values must agree before
> ?convergence? is reached. (Units for this field is Watts.) Field: Temperature
> Convergence This value represents the number at which the zone temperatures must
> agree (from previous iteration) before ?convergence? is reached. (Units for this
> field is delta C)." is it correct? or am i wrong? thanks all O.Gocer
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/