There are several ways in which EnergyPlus can control humidity and temperature
at the same time depending on the system type.
For chilled water systems, cool-reheat control of chilled water coils is
currently available to meet humidity control requirements (see
5ZoneWaterCooled_HighRHControl.idf example file).
For DX coils, cool-reheat (FurnaceWithDXSystemRHcontrol.idf, or using
DXSystem:Airloop - no example but similar to SmOffPSZ-MultiModeDX.idf - new in
v1.2.2) and a 2-position coil bypass or sub-cool reheat option is also
available (SmOffPSZ-MultiModeDX.idf - new in v1.2.2).
Plus a desiccant dehumidifier can be used to control humidity
(DesiccantCVRhZoneRHCtrl.idf).
A variable bypass for chilled water coils is under development, planned for the
Fall 2005 release.
Mike
On 26 Apr 2005, at 0:03, t_graham_carter wrote:
>
>
> Dear All,
> I've had a search through the message archive on a number of keywords
> with no hits that directly answer my question.
>
> My exposure to E+ has been limited to a recent two day workshop and
> skimming of various technical reports / documents on the software's
> development so I apologise for any dumb questions.
>
> From the workshop it is my understanding that you have a supply side
> and a demand side of loops be it an air or water loop. In the case of
> air loops you can control supply temperature to meet the zone of
> greatest demand (based on a calculated load as opposed to a return or
> room temperature). I believe you can also control the supply side
> humidity off of the connecting nodes (between supply and demand loops)
> humidity or temperature (either supply or return node). But you cannot
> not currently achieve the two togeher within E+?
>
> For passive / active chilled beams and chilled ceiling systems and in
> particular for underfloor air conditioning systems, there are good
> reasons to independently control supply humidity and temperature via
> face and bypass dampers on a cooling coil(s). I understand that this
> type of control would require a Spark module to be developed (well
> beyond my current knowledge)?
>
> The introduction of nodes and loops in E+ is a key area where E+ can
> distinguish itself from DOE-2.2. However, the limitations of TAS or
> Apache (IES) aside, these two packages allow relative freedom in
> achieving the bypass control noted above. I suspect there are other
> packages that also allow greater freedom in controls than currently
> allowed for in E+.
>
> Are there plans to address these issues within E+ or current work
> arounds? Or would a Spark module be easier to develop / utilise than I
> currently fear?
>
> Regards,
> Graham
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/