Re: [EnergyPlus_Support] Illuminance measurement
In the Engineering Reference, see the section "Lighting Control System
Simulation", starting on p. 125 (pdf p. 153, v1.2.2). The key statement is:
"This relationship assumes that the electric lights at full power produce an
illuminance equal to Iset at the reference point."
EnergyPlus does not simulate the light output of the electric lighting. The
lighting is controlled only by the illuminance provided by daylighting at the
reference point(s). This available illuminance is then entered into the
control relationship depending on the control type and a lighting power
fraction is calculated. So it is assumed that the daylighting sensor cannot
see any output from the artificial lights. How this would be done physically,
I do not know, I am not familiar with actual daylighting controls.
Mike
On 4 May 2005, at 23:14, Fábyo Luiz Pereira wrote:
> Dear all,
>
> How is determined the "Ltg Power Multiplier from Daylighting" if the
> daylight sensors only measures daylight illuminance? I mean, where is measured
> the artificial illuminance from lights? This is measured (calculated by E+) but
> can't be reported?
>
> For example, if I want 500 lux in one environment and the sensor is
> measuring 400 lux, lights will contribute with 100 lux. This artificial
> illuminance to reach the 500 lux is given by E+ as lights electric consumption.
> So, if the electric consumption fluctuates all day long, and in fact this
> happens, means that daylight illuminance is fluctuating.
>
> Thanks!
>
> ________________________________________________________
> Engº Fábyo Luiz Pereira
> UFRGS - Laboratório de Vapor e Refrigeração
> Rua Sarmento Leite, 425 - Sala 203 - Centro - 90050-170
> Fone / Fax: +55 51 3316-3167 / 3316-3355
> www.mecanica.ufrgs.br/lafrig
> Porto Alegre - RS - BRASIL
>
>
>
>
>
> Yahoo! Acesso Grátis - Internet rápida e grátis.
> Instale o discador agora! http://br.acesso.yahoo.com/
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/