Re: [EnergyPlus_Support] Relationship between G-C and Conductivity
>From the DOE-2.1 Reference Manual, p. III.49:
GLASS-CONDUCTANCE is used to specify the heat conductance of the total window
except for the outside film coefficient.
This keyword is part of the GLASS-TYPE command which describes a complete
window construction which may be made of 1 or more panes (layers) of glass.
In EnergyPlus, MATERIAL:WINDWOGLASS describes a single layer (pane) of glass.
The Conductivity of this layer is just the conductivity of the glass and does
not include interior or exterior film (convection) coefficients.
For a single-pane window, EnergyPlus-MATERIAL:WINDWOGLASS-Conductivity would be
equal to the equivalent DOE-2.1E-GLASS-CONDUCTANCE minus the inside film
coefficient.
For multi-pane windows, the DOE-2.1E value is the conductance of all glass
panes and all air gaps combined, so it is very different from the EnergyPlus
Conductivity.
Mike
On 11 May 2005, at 2:30, beyangj wrote:
> Dear,
> I want to know what's the relationship between the Glass-Conductance in
> the DOE2.1E INP file and the Conductivity {W/m-K} in the
> MATERIAL:WINDOWGLASS in the IDF file of Energyplus. Could you tell me
> the relationship between them?
>
> Best,
>
> Stewart
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/