Thanks Peter (Ellis). The criteria are described quite well in the
Engineering Document under the heading "Time-Step Luminance".
The reference is Perez et alia, "Modeling Daylight Availability and
Irradiance Components from Direct and Global Irradiance",
Solar Energy 44, pp 271-289, 1990.
Fred Buhl
Ellis, Peter wrote:
>
>Hello Peter,
>
>The sky type is selected using a sky weighting factor determined by SkyClearness and SkyBrightness:
>
>3.0 < SkyClearness < 4.0 --> interpolate between "clear sky" and "clear turbid sky"
> SkyWeight = MIN(1.0,(SkyClearness-3)/3)
> ...if SkyWeight = 1, then it's a clear sky
>
>1.2 < SkyClearness < 3.0 --> interpolate between "clear turbid sky" and "intermediate sky"
> SkyWeight = (SkyClearness - 1.2)/1.8
> ...if SkyWeight = 1, then it's a clear turbid sky
>
>1.0 < SkyClearness < 1.2 --> interpolate between "intermediate sky" and "overcast sky"
> SkyWeight = MIN(1.0, MAX(0.0, (SkyClearness-1)/0.2, (SkyBrightness-0.05)/0.4))
> ...if SkyWeight = 1, then it's an intermediate sky
> ...if SkyWeight = 0, then it's an overcast sky
>
>
>"Sky Clearness for Daylighting Calculation" and "Sky Clearness for Daylighting Calculation" are output variables that you can report out, if you wish.
>
>The final daylighting factors are interpolations/weighted averages (using SkyWeight) between the daylight factors calculated for each discrete sky type.
>
>SkyClearness is calculated using BeamSolarRad and DifSolarRad come from the weather file:
>
> Zeta = 1.041*SunZenith**3
> SkyClearness = ( (DifSolarRad + BeamSolarRad)/(DifSolarRad + 0.0001) + Zeta )/(1.+Zeta)
>
>
>SkyBrightness is calculated as follows:
>
>SkyBrightness = (DifSolarRad * 93.73)* AirMass / ExtraDirNormIll(Month)
>
>REAL, PARAMETER, DIMENSION(12) :: ExtraDirNormIll= & ! Monthly exterrestrial direct normal illuminance (lum/m^2)
> (/131153.,130613.,128992.,126816.,124731.,123240., &
> 122652.,123120.,124576.,126658.,128814.,130471./)
>
>
>Let me know if you have further questions.
>
>Peter Ellis
>NREL
>
>
>-----Original Message-----
>From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of Peter G. Loutzenhiser
>Sent: Wednesday, May 11, 2005 1:54 AM
>To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>Subject: [EnergyPlus_Support] Daylighting
>
>
>Dear All,
>
>I am interested in the daylighting algorithm described in the Engineering
>Auxillary manual and by Winkelmann and Sellkowitz (1985). What is the
>criterion (or what are the criteria) for selecting the sky conditions (there
>are four in EnergyPlus and two in DOE-2.1e), and what specific parameters are
>these conditions a function of?
>
>Many thanks,
>
>Peter
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>
>
>
> _____
>
>Yahoo! Groups Links
>
>
>* To visit your group on the web, go to:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>* To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>
>
>* Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> .
>
>
>
>
>[Non-text portions of this message have been removed]
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/