[EnergyPlus_Support] About the WindAC
Dear,
I'm doing a simulation for a residential building. The window air
conditioner model in EnergyPlus is "cooling only", but there need
heating in the winter in my model, so I chose the
COIL:ELECTRIC:HEATING for heating, and the
COIL:DX:CoolingBypassFactorEmpirical is followed by the
COIL:ELECTRIC:HEATING.
When I set the items as follow,
NODE LIST,
GAB1Inlets, !- Node List Name
GAB1 Heating Coil Outlet Node; !- Node_ID_1
NODE LIST,
GAB1Exhausts, !- Node List Name
GAB1WindACAirInletNode; !- Node_ID_1
COIL:Electric:Heating,
GAB1 Heating Coil, !- Coil Name
HEAT-SCHED-B1, !- Available Schedule
1, !- Efficiency of the Coil
autosize, !- Nominal Capacity of the Coil {W}
GAB1WindACAirOutletNode, !- Coil_Air_Inlet_Node
GAB1 Heating Coil Outlet Node; !- Coil_Air_Outlet_Node
COIL:DX:CoolingBypassFactorEmpirical,
GAB1WindACDXCoil, !- Coil Name
System Available Schedule-B1, !- Availability Schedule
autosize, !- Rated Total Cooling Capacity (gross)
{W}
autosize, !- Rated SHR
3.0, !- Rated COP
autosize, !- Rated Air Volume Flow Rate {m3/s}
GAB1WindACFanOutletNode, !- Coil Air Inlet Node
GAB1WindACAirOutletNode, !- Coil Air Outlet Node
WindACCoolCapFT, !- Total Cooling Capacity Modifier Curve
(function of temperature)
WindACCoolCapFFF, !- Total Cooling Capacity Modifier Curve
(function of flow fraction)
WindACEIRFT, !- Energy Input Ratio Modifier Curve
(function of temperature)
WindACEIRFFF, !- Energy Input Ratio Modifier Curve
(function of flow fraction)
WindACPLFFPLR, !- Part Load Fraction Correlation
(function of part load ratio)
CycFanCycComp; !- Supply Air Fan Operation Mode
AIR CONDITIONER:WINDOW:CYCLING,
GAB1WindAC, !- name of window AC unit
System Available Schedule-B1, !- availability schedule
autosize, !- maximum air flow rate {m3/s}
autosize, !- maximum outside air flow rate {m3/s}
GAB1WindACAirInletNode, !- air inlet node
GAB1WindACAirOutletNode, !- air outlet node
GAB1WindACOAInNode, !- outside air node
GAB1WindACExhNode, !- air relief node
GAB1WindACOAMixer, !- outside air mixer name
GAB1WindACFan, !- fan name
GAB1WindACDXCoil, !- DX cooling coil name
CycFanCycComp, !- operation mode
blow through, !- fan placement
0.001, !- Cooling Convergence Tolerance
COIL:DX:CoolingBypassFactorEmpirical; !- Cooling coil type
there were such error messages as follow in the ERR file after
running the IDF file,
** Severe ** Error in Node="GAB1 HEATING COIL OUTLET NODE",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=GAB1
************* No node connection errors were found.
** Warning ** The following lines are "Orphan Objects". These
objects are in the idf
** ~~~ ** file but are never obtained by the simulation and
therefore are NOT used.
** ~~~ ** See InputOutputReference document for more details.
************* Object=COIL:ELECTRIC:HEATING=GAB1 HEATING COIL
I just found the item definitions in Air Conditioner:Window:Cycling
are that the air inlet node should be one of the zone exhaust nodes
for the zone which the window air conditioner is cooling, and the air
outlet node should be one of the inlet air nodes for the zone which
is being cooled. I wondered whether I can add the
COIL:ELECTRIC:HEATING to the window air conditioner system. If so,
how can I connect them? Thanks in advance!
Best,
Stewart
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/