Re: [EnergyPlus_Support] About the heat recovery set up
Hello,
In development we are heading towards a general loop structure and not
specifically typed loops. We view loops as a collection of piping that
allows fluid to flow through and connects components. Thinking in this
manner the heat recovery loop object has been obsoleted and replaced with
the more general loop structure connecting components together that can
facilitate heat recovery. We have several example files that show this:
HeatRecoveryElectricChiller.idf
HeatRecoveryPlantLoop.idf
HeatRecoverywithStorageTank.idf
Yes, the water heater was used in these examples to allow for storage of
the recovered heat, but that is not necessary. You could connect the heat
recovered from generators directly to heating coils, for instance.
You can look in the Engineering Documentation in the "Heat Recovery Loop
Systems" section for more information.
Thanks Richard Liesen
At 08:21 AM 5/16/2005, you wrote:
>Dear All
>
> Is there any plant equipment that is able to use the heat recovery
>loop to recover energy from other equipment other than water heater?
> And I look into the heat recovery example file in E+. It is strange
>that the example uses plant loop rather heat recovery loop to set up
>the heat recovery loo. Does it mean that the heat recovery object in
>the plant-condenser loops is unusable right now?
> If I am wrong, could you please give me another example file which
>uses the heat recovery loop to specify the loop?
>
> Thank you in advance:)
>
> charlie
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files area of the Support Web Site.
>
>Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/