Dear Mike
Could please tell me some methods to controll the leaving
temperature of chiller and let it float in a range.
Thank you in advance.
charlie
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> With dual setpoints, EnergyPlus would use the upper setpoint to
control
> chillers, and the lower setpoint to control boilers. EnergyPlus
will not
> control chillers to float within a range as described below.
>
> Mike
>
>
> On 12 May 2005, at 6:39, energypluser wrote:
>
> > Dear all:
> >
> > I set the chiller evaporator outlet node for the Loop
Temperature
> > Setpoint Node in Plant-Condenser Loops. And the setpoint manager
for
> > this node is a dual setpoint manager with the low and high
scheduled
> > temperature at 7C and 13C for all days respectively.
> > The purpose of using this setpoint manager is to let the
chilled
> > water outlet temperature varies between the deadband. But the
> > simulation results show that the chiller supply temperature is
10C,
> > which is the average value of the upper and lower temperature
limit.
> > Is E+ able to control the chiller water supply temperature in
this
> > way?
> > Thank you in advance!
> >
> > charlie
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/