Dear Mike
I wonder whether the temeperture will vary in the time step when
I set up the temperature schedule varying ?
Thank you in advance
charlie
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "applezealot"
<applezealot@y...> wrote:
> Dear Mike
>
> Could please tell me some methods to controll the leaving
> temperature of chiller and let it float in a range.
> Thank you in advance.
>
> charlie
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@g...> wrote:
> > With dual setpoints, EnergyPlus would use the upper setpoint to
> control
> > chillers, and the lower setpoint to control boilers. EnergyPlus
> will not
> > control chillers to float within a range as described below.
> >
> > Mike
> >
> >
> > On 12 May 2005, at 6:39, energypluser wrote:
> >
> > > Dear all:
> > >
> > > I set the chiller evaporator outlet node for the Loop
> Temperature
> > > Setpoint Node in Plant-Condenser Loops. And the setpoint
manager
> for
> > > this node is a dual setpoint manager with the low and high
> scheduled
> > > temperature at 7C and 13C for all days respectively.
> > > The purpose of using this setpoint manager is to let the
> chilled
> > > water outlet temperature varies between the deadband. But the
> > > simulation results show that the chiller supply temperature is
> 10C,
> > > which is the average value of the upper and lower temperature
> limit.
> > > Is E+ able to control the chiller water supply temperature in
> this
> > > way?
> > > Thank you in advance!
> > >
> > > charlie
> > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> appropriate folder
> > > in the Files area of the Support Web Site.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@g...
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.