In some systems, the cooling coil model may generate such errors during initial
iterations at very low load conditions. Which cooling coil model are you
using? What is the min actuated flow rate in the controller for this coil? If
it is zero, try setting it to a small value, such as 0.00001. If this does not
help, please post the input file.
Mike
On 23 May 2005, at 15:03, Ali_Ajmi wrote:
> Dear All,
>
> I have created file of office building with five zone, this file was made to run
> without any errors or warning. The load was covered by purchased air now I
> replace it with VAV system. Now there some sort of error which i could not
> figure out their sources:
>
> ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30
> ** ~~~ ** Enthalpy=-699562.92274 Pressure= 99433.54 ** ~~~ **
> Initial Resultant Temperature= -59.98 ** Warning ** Temperature out of range
> [-100. to 200.] (PsyPsatFnTemp) ** ~~~ ** Occurrence info=CHICAGO
> ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~ ** Input Temperature=-711.86
> ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp) **
> ~~~ ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 **
> ~~~ ** Input Temperature=-713.97 ** Warning ** Temperature out of range
> [-100. to 200.] (PsyPsatFnTemp) ** ~~~ ** Occurrence info=CHICAGO
> ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~ ** Input Temperature=-713.98
> ** Warning ** Calculated Relative Humidity out of range (PsyRhFnTdbWPb) **
> ~~~ ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 **
> ~~~ ** Dry-Bulb= -713.98 Humidity Ratio= 1.000E-005 Calculated Relative
> Humidity (fraction)= 940.37 ** ~~~ ** Relative Humidity being reset to
> 1.0 ** Warning ** Enthalpy out of range (PsyTsatFnHPb) ** ~~~ **
> Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~ **
> Enthalpy=-699562.92274 Pressure= 99433.54 ** ~~~ ** Initial Resultant
> Temperature= -59.98 ** Warning ** Temperature out of range [-100. to 200.]
> (PsyPsatFnTemp) ** ~~~ ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21
> 18:15 - 18:30 ** ~~~ ** Input Temperature=-711.86 ** Warning **
> Temperature out of range [-100. to 200.] (PsyPsatFnTemp) ** ~~~ **
> Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~ **
> Input Temperature=-713.97 ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30
> ** ~~~ ** Enthalpy=-699562.92274 Pressure= 99433.54 ** ~~~ **
> Initial Resultant Temperature= -59.98 ** Warning ** Temperature out of range
> [-100. to 200.] (PsyPsatFnTemp) ** ~~~ ** Occurrence info=CHICAGO
> ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~ ** Input Temperature=-711.86
> ** Warning ** Calculated Relative Humidity out of range (PsyRhFnTdbWPb) **
> ~~~ ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 **
> ~~~ ** Dry-Bulb= -713.98 Humidity Ratio= 1.000E-005 Calculated Relative
> Humidity (fraction)= 940.37 ** ~~~ ** Relative Humidity being reset to
> 1.0 ** Warning ** Enthalpy out of range (PsyTsatFnHPb) ** ~~~ **
> Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~ **
> Enthalpy=-699562.92274 Pressure= 99433.54 ** ~~~ ** Initial Resultant
> Temperature= -59.98 ** Warning ** Enthalpy out of range (PsyTsatFnHPb) **
> ~~~ ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 **
> ~~~ ** Enthalpy=-699562.92274 Pressure= 99433.54 ** ~~~ ** Initial
> Resultant Temperature= -59.98 ** Warning ** Calculated Relative Humidity out
> of range (PsyRhFnTdbWPb) ** ~~~ ** Occurrence info=CHICAGO ILLINOIS
> SUMMER, 07/21 18:15 - 18:30 ** ~~~ ** Dry-Bulb= -713.98 Humidity Ratio=
> 1.000E-005 Calculated Relative Humidity (fraction)= 940.37 ** ~~~ **
> Relative Humidity being reset to 1.0 ** Warning ** Enthalpy out of range
> (PsyTsatFnHPb) ** ~~~ ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21
> 18:15 - 18:30 ** ~~~ ** Enthalpy=-699562.92274 Pressure= 99433.54 **
> ~~~ ** Initial Resultant Temperature= -59.98 ** Warning ** Calculated
> Relative Humidity out of range (PsyRhFnTdbWPb) ** ~~~ ** Occurrence
> info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~ ** Dry-Bulb=
> -713.98 Humidity Ratio= 1.000E-005 Calculated Relative Humidity (fraction)=
> 940.37 ** ~~~ ** Relative Humidity being reset to 1.0 ** Warning **
> Calculated Relative Humidity out of range (PsyRhFnTdbWPb) ** ~~~ **
> Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~ **
> Dry-Bulb= -713.98 Humidity Ratio= 1.000E-005 Calculated Relative Humidity
> (fraction)= 940.37 ** ~~~ ** Relative Humidity being reset to 1.0 **
> Warning ** Calculated Relative Humidity out of range (PsyRhFnTdbWPb) ** ~~~
> ** Occurrence info=CHICAGO ILLINOIS SUMMER, 07/21 18:15 - 18:30 ** ~~~
> ** Dry-Bulb= -713.98 Humidity Ratio= 1.000E-005 Calculated Relative Humidity
> (fraction)= 940.37 ** ~~~ ** Relative Humidity being reset to 1.0
> ************* Psychrometric Error Summary ************* Routine - Number of
> errors ************* PsyTdpFnTdbTwbPb-0 *************
> PsyRhFnTdbWPb-3970 ************* PsyTwbFnTdbWPb-0 *************
> PsyVFnTdbWPb-0 ************* PsyWFnTdpPb-0 ************* PsyWFnTdbH-0
> ************* PsyWFnTdbTwbPb-0 ************* PsyWFnTdbRhPb-0
> ************* PsyPsatFnTemp-960 ************* PsyTsatFnHPb-7940
> ************* PsyTsatFnPb-0 ************* tp12c0-0 *************
> tp12c1-0 ************* tp12h0-0 ************* tp12h1-0 *************
> freeze-0 ************* EnergyPlus Completed Successfully-- 21 Warning; 0
> Severe Errors; Elapsed Time=00hr 15min 8.00sec
>
> Best Regards
> Ali
>
>
>
> ---------------------------------
> Yahoo! Messenger - want a free & easy way to contact your friends online?
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/