My guess is that the outside air controller actuated node is pointing to the oa
inlet node on the mixing box, but it should be pointing to the OA inlet node to
the heat exchanger. From the Input Output Reference for the OA controller:
Field: Actuated_Node
The name of the node that is associated with the outside air damper. This
should be the outermost air node on the outside air path connected to the
outside air stream for the mixer associated with this outside air controller.
Mike
On 3 Jun 2005, at 12:24, Richard Raustad wrote:
> The example file TermRhGenericOAHeatRecMinExh.idf is very similar to the
> configuration shown below. Please review this example file for
> assistance configuring the air loop.
>
> massimiliano_scarpa wrote:
>
> > Good morning to You All.
> > After a long time, I'm coming back to EPlus.
> > I'm beginning with an easy system.
> > I've just uploaded the file "Vigonza_Tutta aria con OA e HR.zip"
> >
> > This system consists in:
> > 1) An air loop composed by:
> > HEAT EXCHANGER:AIR TO AIR:FLAT PLATE
> > OUTSIDE AIR MIXER
> > FAN:SIMPLE:VariableVolume
> > COIL:Water:Cooling
> > COIL:Water:SimpleHeating
> > Direct Air
> > Zone 0_Serv
> > 2) Hot water plant loop composed by:
> > PURCHASED:HOT WATER
> > COIL:Water:SimpleHeating
> > 3) Chilled water plant loop composed by:
> > PURCHASED:CHILLED WATER
> > COIL:Water:Cooling
> >
> > I'm beginning applying the system to one zone.
> > I'm going to feed the air loop with 100% outside air.
> > The only problem with this system is that the air loop never
> > receives outside air. I tried many ways, but the result is always
> > the same: the outside air flow rate is 0 m3/s, even if the minimum
> > outside air flow rate (in CONTROLLER:OUTSIDE AIR) is equal to the
> > maximum outside air flow rate.
> > For the mixed air set point (Node AL_FVV_IN), I used a SETPOINT
> > MANAGER:SCHEDULED with the fixed temperature -15°C. In the previous
> > attempts I used different SetPoint Manager, but they gave the same
> > result. As a matter of fact, they should not modify the situation,
> > since the minimum outside air flow rate and the maximum one are
> > equal.
> > I will be grateful to anybody will be able to help me.
> > Thank You in advance
> >
> > Best regards
> >
> > Massimiliano
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files area of the Support Web Site.
> >
> >
> >
> > ------------------------------------------------------------------------
> > Yahoo! Groups Links
> >
> > * To visit your group on the web, go to:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > * To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
> > be>
> >
> > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > Service <http://docs.yahoo.com/info/terms/>.
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/