Re: [EnergyPlus_Support] Fan Coil Unit : 4 Pipe
Use the 4-pipe fan coil object, and set the availability schedules on the
heating coil and cooling coil so that only one can be active at any given time.
Mike
On 16 Jun 2005, at 21:00, marieodeline wrote:
> Dear all,
>
> I would like to know if it is possible to create a Fan Coil Unit : 2
> Pipe, with energy plus.
> Thank you in advance for your answers.
> Marie Odeline
>
>
>
>