Antw: Re: [EnergyPlus_Support] Base surface does not surround subsurface
Hi Linda,
I didn't unterstand this behavior. The original coordinates are in LLC, CCW.
You have changed the starting point only to get rid of the warning. But you can't say the vertex 4 is the lower left! Because the surface is horizontal and the docu says that for horizontal surfaces the starting point doesn't matter. Or is the statement in the docu simply wrong?
Christian
>>> linda@xxxxxxxxxx 28.06.2005 19:20 >>>
Hi Christian,
I believe it's that your roof coordinates are not in the LLC, CCW, relative
terms as set in the surfacegeometry.
If you put the roof in as:
SURFACE:HEATTRANSFER,
G.000.Roof.5, !- User Supplied Surface Name
Roof, !- Surface Type
massive roof, !- Construction Name of the Surface
G.000, !- InsideFaceEnvironment
ExteriorEnvironment, !- OutsideFaceEnvironment
, !- OutsideFaceEnvironment Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.0000, !- View Factor to Ground
4, !- Number of Surface Vertex Groups -- Number
of (X,Y,Z) groups in this surface
-4.000000000000000e+000,9.999999999999998e-002,3.000000000000000e+000,
!- X,Y,Z ==> Vertex 4
0.000000000000000e+000,0.000000000000000e+000,3.000000000000000e+000,
!- X,Y,Z ==> Vertex 1
0.000000000000000e+000,4.100000000000000e+000,3.000000000000000e+000,
!- X,Y,Z ==> Vertex 2
-4.000000000000000e+000,4.100000000000000e+000,3.000000000000000e+000;
!- X,Y,Z ==> Vertex 3
The error message goes away.
(Note I just used yours so the Vertex comments are incorrect).
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/