[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Error message on flow rate
Well, I figured this problem out. I did not include the hot and
chilled water demand bypass branch in the splitter.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "zhaicq98" <zhaicq98@y...>
wrote:
> I think I have corrected the error in the air loop. I have put the
> return fan as part of the outside air system. I think it should
work
> in this way. However, the water flow rate error remains. I really
> have no idea what to do with regard to it.
>
> Thanks,
> Chaoqin
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "zhaicq98"
<zhaicq98@y...>
> wrote:
> > Hi, Linda,
> >
> > Thanks for your response. I have a question regarding the air
loop
> > you mentioned.
> >
> > I have a supply fan and a return fan in the system. What I did is
> to
> > put the supply fan in one branch (main air loop branch), and the
> > return fan in another (return air branch). The primary air loop
> > consists of these two branches. I think the outlet from the
return
> > air branch is the return air inlet for the outside air system of
> the
> > main air loop branch. If this is not the correct way to do it,
> could
> > you please let me know what I should do?
> >
> > Thanks again,
> > Chaoqin
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie
> <linda@l...>
> > wrote:
> > > See if this further error detection will help you:
> > >
> > > Program Version,EnergyPlus 1.2.2.033, 7/17/2005 4:28
> PM,IDD_Version
> > 1.2.2.033
> > > ** Warning ** No Controllers for Air System:AHU37 PRIMARY
AIR
> > LOOP
> > > ** Severe ** Inlet parameters for plant demand side
splitter
> > are
> > > not physically possible
> > > ** ~~~ ** Problem in input for plant demand side HOT
> WATER
> > PLANT LOOP
> > > ** ~~~ ** The maximum flow out of the splitter [10.45]
is
> > > less than the minimum inlet flow [15.86]
> > > ** ~~~ ** Flow rate inputs for the loop do not match
flow
> > > requirements of the various branches/components
> > > ** ~~~ ** Check your flow rates and make sure that flow
> > > balances between the splitter inlet and outlets
> > > ** Fatal ** EnergyPlus terminated due to reason stated
above
> > > ************* Fatal error -- final processing. More error
> > > messages may appear.
> > > ************* Testing Individual Branch Integrity
> > >
> > > =====> especially this:
> > > ** Severe ** Non-unique node name found, name=AHU37 RETURN
> AIR
> > INLET
> > > ** ~~~ ** ..1st occurence in Branch=AHU37 MAIN AIR LOOP
> > BRANCH
> > > ** ~~~ ** ..duplicate occurrence in Branch=AHU37 RETURN
> AIR
> > BRANCH
> > > ** Severe ** Branch(es) did not pass integrity testing
> > >
> > >
> > > Linda
> > >
> > > EnergyPlus WebSite: http://www.energyplus.gov
> > > Owner: EnergyPlus_Support list
> > > Member: EnergyPlus Development Team
> > >
> > >
> > >
> > > [Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/