RE: [EnergyPlus_Support] Re: zoning without walls
Brent
Now that the HVAC system doesn't not consider the geometric details
of the thermal zone, can I specify the input data of the terminals
in each ficitional zone by atuosizing?
[Griffith, Brent]
Yes. But the zones aren't any more "fictional" than completely closed zones. They are an important part of the model. Thermal zones are a very real thing in designing HVAC distribution and control systems, even in an open floor plan.
If I want to output the cooling&heating demand of each zone for
comparision, how can I get the specified data for each zone?
[Griffith, Brent]
EnergyPlus has many report variables that are available for each zone. Check the .rdd file (one of the outputs from running EnergyPlus) for a listing of available report variables.
The
terminal's outuput would be unknown because the HVAC system in E+
can not be implemented in fixed location.
Thank you in advance
[Griffith, Brent]
I guess you are worried about the terminal units actually having an affect on the neighboring zones in the open plan. This is why you want to add a pair of "Mixing" objects. Remember that E+ is a simplified engineering model. If you really need to model indoor air distibution in detail then you would have to go with CFD.
charlie
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/