Re: [EnergyPlus_Support] system sizing warning



At 11:10 PM 7/31/2005, energypluser wrote:
>I linked a vav terminal to an air-to-air heatpump. I want to use the
>sizing function of E+. But the simulation results show the following
>warning message:
>Input file has requested Sizing Calculations but no Simulations are
>being done. Succeeding warnings/errors may be confusing.

There is nothing to fix.  If you take the results of the sizing 
calculations and plug them into the appropriate spots then you can do 
a simulation.  On the other hand, if you want to see the results of 
the sizing with your input, you should have "Yes" in one of the Run 
Control object fields "Do Design Days" or "Do Weather Simulation".


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12ha7l5fd/M=362131.6882499.7825260.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1122912732/A=2889191/R=0/SIG=10r90krvo/*http://www.thebeehive.org
">Get Bzzzy! (real tools to help you find a job) Welcome to the Sweet Life - brought to you by One Economy</a>.</font>
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/