Dear Mike,
Thank you for the explanation!
Wah
こんにちは。
In message "Re: [EnergyPlus_Support] Purchase Air problem 2",
Michael J. Witte wrote...
>
>
>On 29 Jul 2005, at 17:45, wah wrote:
>
>> Dear Mike,
>>
>> I would like to refer to an example day, 7th Jan.
>>
>> For LVG zone, the Heating Thermostat is set to 20C (Control Type 1) during hours
>> 9-11, 13, 14, 19-23. However, the LVG MAT does not show 20C except for hours 22
>> and 23 (19C, 21C, 24C, 34C, 36C, 25C, 23C, 22C). Even the supply air temperature
>> (Node2) does not show the purchase air supply air temperature, which was set to
>> 40C. For the same day, ADJ zone MAT meets all set point temperature, and the
>> supply air temperature also shows the expected value, 50C.
>
>Control Type 1 = Single Heating Setpoint. The zone temperatures are above the
>heating setpoint, so there is no need for the system to come on. The Purchased
>Air system is not causing the zone to overheat, the combination of internal
>loads and environment loads are making the zone warm with no HVAC heating or
>cooling.
>
>If you want the system to automatically switch between heating and cooling as
>needed, then use Control Type 4 = Dual Setpoint with Deadband at all times.
>
>Mike
>
>
>>
>> The same happens to ADJ zone during cooling period, for example, 2nd July.
>> ADJ MAT is 20, 24, 25, 25, 26 for hours 1 -7, though the cooling setpoint is 28.
>> The supply air node (NodeB) also did not show the expected value, 13C for those
>> hours, although Control Type is 2 and Setpoint shows 28C.
>>
>> I hope this explains my confusion.
>>
>> Please advice and thank you!
>>
>> PuiWah
>>
>>
>>
>>
>>
>>
>> こんにちは。
>>
>> In message "Re: [EnergyPlus_Support] Purchase Air problem 2",
>> Michael J. Witte wrote...
>> >My results look the same as yours. Whenever the control type is set to zero,
>> >the setpoint will not be met, because the thermostat is off. There are times
>> >when the zone is warmer than the heating setpoint or cooler than the cooling
>> >setpoint, but that does not mean the system is not meeting setpoint. > >If you
>> want to maintain the space temperature at all times, then use the DUAL
>> >SETPOINT WITH DEADBAND thermostat control type, so that the system can
>> >automatically switch between heating and cooling as needed. > >If this still
>> does not explain things, please refer to specific times in the >output file in
>> which you see a problem. > >Mike > > >On 26 Jul 2005, at 22:52, wah wrote: > >>
>> Dear Mike, >> >> Thank you for the advice. >> >> The Heating and Cooling
>> Setpoint and Control Type do show up as expected. >> However, the LVG MAT could
>> not meet Heating Setpoint but meet Cooling Setpoint, >> while ADJ MAT meets
>> both setpoints most of the time. >> >> I used the PurchAir Problem idf with
>> JPN_Osaka_IWEC.epw weather file. >> As you mentioned the purchased air is
>> meeting the request, I wonder if we are >> getting the same output files.. I
>> uploaded my output file: >> PurchaseAirProbSpreadsheet Random check shows LVG
>> Purchase Air meets 36% of >> Heating and 100% of Cooling requirement; >>
>> ADJ Purchase Air meets 96% if Heating and 66% of Cooling >>
>> requirement >> I suppose if everything goes well the Heating and
>> Cooling requirement should be >> met at least 80% of the time? >> >> Please
>> advice and thank you! >> >> PuiWah >> >> >> こんにちは。 >> >> In message
>> "Re: [EnergyPlus_Support] Purchase Air problem", >> Michael J. Witte wrote...
>> >> >Add the following report variables to see how the system controls are >>
>> operating: > > Zone/Sys Thermostat Heating Setpoint > Zone/Sys Thermostat >>
>> Cooling Setpoint > Zone/Sys Thermostat Control Type > >Reviewing the results
>> >> shows that the purchased air is meeting these requests. >In the control
>> type >> schedules there are several months where the control type >is being
>> set to zero >> which means no heating or cooling should operate. > >Mike > >
>> >On 25 Jul 2005, >> at 15:31, 黄佩華 wrote: > >> Hello. >> I am using
>> Purchase Air but it >> does not work consistently. >> The Zone MAT meet the
>> setpoint temperature only >> during some days in the >> heating and cooling
>> period. >> Uploaded the file: >> PurchAir Problem >> Could anybody please
>> advice whether it is problem with my >> setting? >> Thank you! >> >> PuiWah >>
>> >> >> >> >> The primary EnergyPlus web >> site is found at: >>
>> http://www.energyplus.gov >> >> The group web site is: >> >>
>> http://groups.yahoo.com/group/EnergyPlus_Support/ >> >> Attachments are not >>
>> allowed -- please post any files to the appropriate folder >> in the Files area
>> >> of the Support Web Site. >> >> Yahoo! Groups Links >> >> >> >> >> >> >> >>
>> > > >> > >======================================================== >Michael J.
>> Witte, >> GARD Analytics, Inc. >EnergyPlus Testing and Support >>
>> >EnergyPlus-Support@xxxxxxxx > > > > >The primary EnergyPlus web site is found
>> >> at: >http://www.energyplus.gov > >The group web site is: >>
>> >http://groups.yahoo.com/group/EnergyPlus_Support/ > >Attachments are not >>
>> allowed -- please post any files to the appropriate folder in the Files area of
>> >> the Support Web >> Site. >> > >> > >> > >> > YAHOO! GROUPS LINKS >>
>> > Visit your group "EnergyPlus_Support" on the web. >> > To unsubscribe
>> from this group, send an email to: >> >
>> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx >> > Your use of Yahoo!
>> Groups is subject to the Yahoo! Terms of Service. >> > >> >> >> >> >> The
>> primary EnergyPlus web site is found at: >> http://www.energyplus.gov >> >> The
>> group web site is: >> http://groups.yahoo.com/group/EnergyPlus_Support/ >> >>
>> Attachments are not allowed -- please post any files to the appropriate folder
>> >> in the Files area of the Support Web Site. >> >> Yahoo! Groups Links >> >>
>> >> >> >> >> >> >> > > >
>> >======================================================== >Michael J. Witte,
>> GARD Analytics, Inc. >EnergyPlus Testing and Support
>> >EnergyPlus-Support@xxxxxxxx > > > > >The primary EnergyPlus web site is found
>> at: >http://www.energyplus.gov > >The group web site is:
>> >http://groups.yahoo.com/group/EnergyPlus_Support/ > >Attachments are not
>> allowed -- please post any files to the appropriate folder in the Files area of
>> the Support Web
>> Site.
>> >
>> >Yahoo! Groups Links
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>>
>>
>>
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the appropriate folder
>> in the Files area of the Support Web Site.
>>
>> Yahoo! Groups Links
>>
>>
>>
>>
>>
>>
>>
>>
>
>
>
>========================================================
>Michael J. Witte, GARD Analytics, Inc.
>EnergyPlus Testing and Support
>EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web
Site.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12huvomrl/M=362335.6886445.7839731.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1123240329/A=2894361/R=0/SIG=13jmebhbo/*http://www.networkforgood.org/topics/education/digitaldivide/?source=YAHOO&cmpgn=GRP&RTP=http://groups.yahoo.com/";>In low income neighborhoods, 84% do not own computers. At Network for Good, help bridge the Digital Divide!</a>.</font>
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/