RE: [EnergyPlus_Support] heating loads



Amit, 
 
I took a very quick look at your file (but didn't run it).  I don't know of a refrigerator that will use 1,040 watts all day long; this could be heating the space.  I would also change to dual heating and cooling setpoint control.  
 
Brent

-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of Amit jain
Sent: Friday, August 05, 2005 1:28 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] heating loads



Thanks for responding. I have checked the internal loads schedules and also the weather data belongs Sterling Va or Washington Dc, which has really cold winters. My model does not involve natural ventilation but a betweenglass shade with airflow.(outside to outside). 

I have posted my file house.idf on the support group files area for further investigation. I am goingout of ideas.

thanks
Amit


Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
If the zone temperature is greater than the thermostat set point 
temperature, the heating rate should be 0. Does your simulation use 
outdoor ventilation air or infiltration? Does the occupants/equipment 
schedules produce enough heat to raise the zone air temperature? Is you 
climate cold enough to require heating? Something in your input deck is 
heating the zone which in turn disables the heating coil.

Search the example files to find a system similar to yours and 
familiarize yourself with that input deck.

If you can't find a solution, upload your input deck to the support 
group files area.

Amit jain wrote:

>
> Hi,
>
> I have built a rather simple purchase air system for a single zone 
> building. The model is not controlling the heating season of the year 
> consitently. It is giving 0 as heating rate for most hours and also, 
> the zone air temp. is shooting high uncontrolably. The cooling cycle 
> is working fine.
>
> I have checked the schedule but it seems fine. Can anyone can give me 
> a direction to investigate further.
>
> thanks
>
> Amit
>
> __________________________________________________
> Do You Yahoo!?
> Tired of spam?  Yahoo! Mail has the best spam protection around
> http://mail.yahoo.com
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the 
> appropriate folder in the Files area of the Support Web Site.
>
>
>
> ------------------------------------------------------------------------
> YAHOO! GROUPS LINKS
>
>     *  Visit your group "EnergyPlus_Support
>       < http://groups.yahoo.com/group/EnergyPlus_Support>" on the web.
>        
>     *  To unsubscribe from this group, send an email to:
>        EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>       <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>        
>     *  Your use of Yahoo! Groups is subject to the Yahoo! Terms of
>       Service < http://docs.yahoo.com/info/terms/>.
>
>
> ------------------------------------------------------------------------
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.




---------------------------------
YAHOO! GROUPS LINKS 


    Visit your group "EnergyPlus_Support" on the web.
  
    To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
  
    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 


---------------------------------



__________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around 
http://mail.yahoo.com 

[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.




  _____  

YAHOO! GROUPS LINKS 


	
*	 Visit your group " EnergyPlus_Support <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
  

*	 To unsubscribe from this group, send an email to:
  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> 
  

*	 Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . 


  _____  




[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12h84274p/M=362335.6886445.7839731.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1123278260/A=2894361/R=0/SIG=13jmebhbo/*http://www.networkforgood.org/topics/education/digitaldivide/?source=YAHOO&cmpgn=GRP&RTP=http://groups.yahoo.com/";>In low income neighborhoods, 84% do not own computers. At Network for Good, help bridge the Digital Divide!</a>.</font>
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/