Re: [EnergyPlus_Support] Frame Effects
Peter,
EnergyPlus uses 2.5 inches = 63.55 mm for the frame edge width, which is
pretty close to
65 mm. This value is hardwired in the program and is not a user input.
Fred Buhl
Peter G. Loutzenhiser wrote:
>Dear All,
>
>I am looking over the calculation procedure for the glazing heat balance
>equation and in the Engineering Manual it shows the calcutions. One value that
>I am very interesting in is the "Ratio of Frame-Edge Glass Conductance" which
>is an input into EnergyPlus used to quantify the edge effects. According to
>the Engineering Manual, this values is used in conjunction with an edge area.
>To calculate this value required a frame edge distance. Ashrae fundamental
>suggests a common value for this glazing is 65 mm from the frame.
>Unfortunately I have not been able to find what the standard value EnergyPlus
>uses to calculate this ratio, because apparently it is not an input to the
>code. Is this the value the EnergyPlus uses? If not, what value or how does
>it calculated or if I have missed somewhere in the EnergyPlus literature, what
>is the value?
>
>Many thanks,
>Peter
>
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12h4p3nk2/M=362329.6886308.7839368.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1123792075/A=2894321/R=0/SIG=11dvsfulr/*http://youthnoise.com/page.php?page_id=1992
">Fair play? Video games influencing politics. Click and talk back!</a>.</font>
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/