Re: [EnergyPlus_Support] Cooling coil type of Fancoil unit?



To get rid of the error, check the zone sizing report.  Does the zone served by 
this fan coil unit have a non-zero design cooling load?  If not, check 
thermostat schedules, internal loads, etc. to determine whether it should.

Mike


On 24 Aug 2005, at 6:52, Linda Lawrie wrote:

> It might be that the error messages are mixed up though I quickly 
> scanned the code and didn't find it to be true.
> 
> At 03:44 AM 8/24/2005, hbn_pch wrote:
> 
> >  ** Warning ** The design coil load is zero for
> >COIL:Water:SimpleCooling 1F_15_FANCOILCOOLINGCOIL
> >    **   ~~~   ** The autosize value for max water flow rate is zero
> >    **   ~~~   ** To change this, input a value for UA, change the
> >cooling design day, or lower
> >    **   ~~~   **   the zone cooling design supply air temperature
> >
> >    According to the warning, i search the 1F_15_FANCOILCOOLINGCOIL
> >coil and found its type is COIL:Water:Cooling.There is no
> >COIL:Water:SimpleCooling type at all.
> >
> 
> Please submit your code so that we can see if this warning is in 
> error.   Are you saying that your run was successful?
> 
> 
> Linda
> 
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12hca3r4q/M=362335.6886445.7839731.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1124942471/A=2894361/R=0/SIG=13jmebhbo/*http://www.networkforgood.org/topics/education/digitaldivide/?source=YAHOO&cmpgn=GRP&RTP=http://groups.yahoo.com/";>In low income neighborhoods, 84% do not own computers. At Network for Good, help bridge the Digital Divide!</a>.</font>
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/