Re: [EnergyPlus_Support] Re: Cooling coil type of Fancoil unit?



When I run your input file (V1.2.2.030), I get the following in 
warning messages:

    ** Warning ** The design coil load is zero for COIL:Water:Cooling 
RESISTIVE ZONE_FANCOILCOOLINGCOIL
    **   ~~~   ** The autosize value for max water flow rate is zero
    ** Warning ** The design coil load is zero for 
COIL:Water:SimpleHeating RESISTIVE ZONE_FANCOILHEATINGCOIL
    **   ~~~   ** The autosize value for max water flow rate is zero
    **   ~~~   ** To change this, input a value for UA, change the 
heating design day, or lower
    **   ~~~   **   the system heating design supply air temperature
    ** Warning ** The design coil load is zero for COIL:Water:Cooling 
EAST ZONE_FANCOILCOOLINGCOIL
    **   ~~~   ** The autosize value for max water flow rate is zero
    ** Warning ** The design coil load is zero for 
COIL:Water:SimpleHeating EAST ZONE_FANCOILHEATINGCOIL
    **   ~~~   ** The autosize value for max water flow rate is zero
    **   ~~~   ** To change this, input a value for UA, change the 
heating design day, or lower
    **   ~~~   **   the system heating design supply air temperature
    ** Warning ** The design coil load is zero for COIL:Water:Cooling 
NORTH ZONE_FANCOILCOOLINGCOIL
    **   ~~~   ** The autosize value for max water flow rate is zero
    ** Warning ** The design coil load is zero for 
COIL:Water:SimpleHeating NORTH ZONE_FANCOILHEATINGCOIL
    **   ~~~   ** The autosize value for max water flow rate is zero
    **   ~~~   ** To change this, input a value for UA, change the 
heating design day, or lower
    **   ~~~   **   the system heating design supply air temperature

None of the above reference Coil:Water:SimpleCooling.

SimpleHeating, yes.  SimpleCooling, no.

There are also lots of Severes of the following nature:
    ** Severe  ** Error in Node="RESISTIVE 
ZONE_FANCOIL_CW_INLET_NODE", Inlet node did not find an appropriate 
matching "outlet" node.
    **   ~~~   ** If this is an outside air inlet node, it must be 
listed in an OUTSIDE AIR INLET NODE LIST object.
    **   ~~~   ** Reference Object=BRANCH, Name=RESISTIVE ZONE_CHWBRANCH
    ** Severe  ** Error in Node="EAST ZONE_FANCOIL_CW_INLET_NODE", 
Inlet node did not find an appropriate matching "outlet" node.
    **   ~~~   ** If this is an outside air inlet node, it must be 
listed in an OUTSIDE AIR INLET NODE LIST object.
    **   ~~~   ** Reference Object=BRANCH, Name=EAST ZONE_CHWBRANCH


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/