RE: ??: Re: [EnergyPlus_Support] Harbour Building



 
Hi Samlee,
Are you using a chiller or a water to water heat pump. In either case the condenser side flow rate is very less as the error indicates 3E-9. if you are using a chiller, please set the condenser side flow rate to autosize. If you are using a heat pump the set a flow rate comparable to the evaporator mass flow rate. The lowest mass flow in E+ is 0.001. Your condenser side setting means that there is no flow in the condenser side. 
 
That should help you solve the problem.
 
Sankar
S.K.Padhmanabhan
Research Associate
Mechanical & Aerospace Engineering
Oklahoma State University,
Stillwater, OK - 74075
Ph: (405)744-4380

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of wing sun lee
Sent: Mon 8/29/2005 11:33 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: ??: Re: [EnergyPlus_Support] Harbour Building



Hi,

How can I address these problem. Would you mind giving me some more hints.

SAMLEE

Linda Lawrie <linda@xxxxxxxxxx> ?:
Will these new warnings help?

    ** Warning ** SizeCondDemandSide: Calculated Plant Sizing Design
Volume Flow Rate=[3.00E-009] is too small. Set to 0.0
    **   ~~~   ** ..occurs for Condenser Loop=CONDENSER WATER LOOP
    ** Warning ** SizeCondSupplySide: Calculated Plant Sizing Design
Volume Flow Rate=[3.00E-009] is too small. Set to 0.0
    **   ~~~   ** ..occurs for Condenser Loop=CONDENSER WATER LOOP
    ** Warning ** SizePump: Calculated Pump Nominal Volume Flow
Rate=[3.00E-009] is too small. Set to 0.0
    **   ~~~   ** ..occurs for Pump=COND CIRC PUMP

At 09:48 AM 8/27/2005, wing sun lee wrote:
>I can't tackle the following "Warning" & "Severe" problems that were
>arisen from my idf file:
>  ** Warning ** Check input. Pump nominal power or motor efficiency
> is set to 0, for pump=COND CIRC PUMP
>    ** Warning ** Check input. Pump nominal volumetric flow rate is
> set or calculated = 0, for pump=COND CIRC PUMP
>    ** Severe  ** COOLING TOWER:SINGLE SPEED "CENTRAL TOWER". Free
> convection air flow rate must be less than the design air flow rate.
>    ** Severe  ** COOLING TOWER:SINGLE SPEED "CENTRAL TOWER". Free
> convection UA must be less than the design tower UA.


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.




---------------------------------
YAHOO! GROUPS LINKS


    Visit your group "EnergyPlus_Support" on the web.
 
    To unsubscribe from this group, send an email to:
 EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
 
    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.


---------------------------------



_______________________________________
 ?????? email ???
 ?? Yahoo! Messenger http://messenger.yahoo.com.hk

[Non-text portions of this message have been removed]




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

Yahoo! Groups Links











[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/