標題: [EnergyPlus_Support] Re: Harbour building



Hi,
 
1.
I have already changed the value of control type from '0' to '1' for the summerdesignday and winterdesignday. However, the warning messages "   ** Warning ** Calculated heating design air flow rate for system=CAV SYSTEM-AHU 1A 1/F is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs." still happened. 
 
2.
How about the "   ** Warning ** Error -- Mass Flow Rate Calculation in Plant Loop=CHILLED WATER LOOP SYS_2, Outlet and Inlet differ by more than tolerance.
   **   ~~~   ** Loop inlet node=CW SUPPLY INLET NODE 2, flowrate=41.7233768353107
   **   ~~~   ** Loop outlet node=CW SUPPLY OUTLET NODE 2, flowrate=39.5427915420240"
 
Regards,
 
SAMLEE

Linda Lawrie <linda@xxxxxxxxxx> 說:
At 07:28 PM 8/31/2005, wing sun lee wrote:

>Hi,
>
>1.
>Thanks for your help.
>You have mentioned that the design control type should not include a 
>"0" control type. However, most of the examples were shown  "0" 
>value at either summerdesignday or winterdesingday. Would you mind 
>giving me an advice to me.

The example files are not always "best practices" though we are 
trying to make them so.  I gave you the advice.   Set up your control 
types on summer/winter design day so they don't include 0.

>
>2a.
>I can't kown how to address these warnings:
>    ** Warning ** Calculated heating design air flow rate for 
> system=CAV SYSTEM-AHU 1A 1/F is zero.
>    **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
>    ** Warning ** Calculated heating design air flow rate for 
> system=VAV SYSTEM-AHU 2B 2/F is zero.
>    **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.

If you do the part in 1 (change control types), these will go away 
(at least they did for me).



Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.




---------------------------------
YAHOO! GROUPS LINKS 


    Visit your group "EnergyPlus_Support" on the web.
  
    To unsubscribe from this group, send an email to:
 EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
  
    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 


---------------------------------



_______________________________________
 想即時收到新 email 通知?
 下載 Yahoo! Messenger http://messenger.yahoo.com.hk 

[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/