[EnergyPlus_Support] Re: Harbour building
At 07:28 PM 8/31/2005, wing sun lee wrote:
>Hi,
>
>1.
>Thanks for your help.
>You have mentioned that the design control type should not include a
>"0" control type. However, most of the examples were shown "0"
>value at either summerdesignday or winterdesingday. Would you mind
>giving me an advice to me.
The example files are not always "best practices" though we are
trying to make them so. I gave you the advice. Set up your control
types on summer/winter design day so they don't include 0.
>
>2a.
>I can't kown how to address these warnings:
> ** Warning ** Calculated heating design air flow rate for
> system=CAV SYSTEM-AHU 1A 1/F is zero.
> ** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
> ** Warning ** Calculated heating design air flow rate for
> system=VAV SYSTEM-AHU 2B 2/F is zero.
> ** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
If you do the part in 1 (change control types), these will go away
(at least they did for me).
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Most low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/