If I understand correctly, this system is supposed to supply a fixed flow rate
at a specified supply temperature rather than adjust supply temperature to
match the zone load.
Assuming that is correct, the problem is that the various setpoint managers are
fighting with each other because the cooling coil and heating coil are using
the same control node. SET POINT MANAGER:SCHEDULED "AHU1 Supply Air Temp
Manager" places a setpoint on "AHU1 Fan Outlet Node". Then SET POINT
MANAGER:SINGLE ZONE MAX HUM "zBaseGalleryStore Max Hum Manager" places a
humidity ratio setpoint on the same node. What is not well-documented is that
the CONTROLLER:SIMPLE resets the control node setpoint if the max humidity
conditions requires more cooling. To see the impact of this, add report
variable "System Node Setpoint Temp" for AHU1 FAN OUTLET NODE.
Because of this, the heating coil controller needs to use a different control
node. An easy solution would be to add "AHU1 HC Outlet Node" to the NODE LIST
for "Supply Air Temp Nodes". And change the AHU1 Heating Coil Controller
control node to be "AHU1 HC Outlet Node". This should solve the problem.
Mike
On 12 Sep 2005, at 14:58, civilnug wrote:
> Hi All,
>
> I've put the above idf in the Problem_Submittals file. In it I have,
> in order, a mixing box, cooling coil, heating coil and humidifier on
> the air loop. This is fed into an area by a direct air system and has
> to have tightly controlled relative humidity levels (50% +/- 5%). The
> system is operating perfectly in winter but my problem is occuring
> during the summer months when attempting to get control of the rh.
>
> The cooling coil kicks in to drag down the temperature below the
> supply air temperature so as to get the humidity ratio to the right
> level, my problem is that the heating coil won't kick in to bring the
> temperature back up to the specified supply air temperature.
>
> Any help would be greatly appreciated.
>
> Regards,
> John McCarthy.
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/