[EnergyPlus_Support] Re: RE:AHU1 Gallery Store PostZTR Hum.idf



Thanks a million Mike, that's been driving me a bit mad for a while 
now. 

Thank you,
John.



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@g...> wrote:
> If I understand correctly, this system is supposed to supply a 
fixed flow rate 
> at a specified supply temperature rather than adjust supply 
temperature to 
> match the zone load.
> 
> Assuming that is correct, the problem is that the various setpoint 
managers are 
> fighting with each other because the cooling coil and heating coil 
are using 
> the same control node.  SET POINT MANAGER:SCHEDULED "AHU1 Supply 
Air Temp 
> Manager" places a setpoint on "AHU1 Fan Outlet Node".  Then SET 
POINT 
> MANAGER:SINGLE ZONE MAX HUM "zBaseGalleryStore Max Hum Manager" 
places a 
> humidity ratio setpoint on the same node.  What is not well-
documented is that 
> the CONTROLLER:SIMPLE resets the control node setpoint if the max 
humidity 
> conditions requires more cooling.  To see the impact of this, add 
report 
> variable "System Node Setpoint Temp" for AHU1 FAN OUTLET NODE.
> 
> Because of this, the heating coil controller needs to use a 
different control 
> node.  An easy solution would be to add "AHU1 HC Outlet Node" to 
the NODE LIST 
> for "Supply Air Temp Nodes".  And change the AHU1 Heating Coil 
Controller 
> control node to be "AHU1 HC Outlet Node".  This should solve the 
problem.
> 
> Mike
> 
> 
> On 12 Sep 2005, at 14:58, civilnug wrote:
> 
> > Hi All,
> > 
> > I've put the above idf in the Problem_Submittals file. In it I 
have, 
> > in order, a mixing box, cooling coil, heating coil and 
humidifier on 
> > the air loop. This is fed into an area by a direct air system 
and has 
> > to have tightly controlled relative humidity levels (50% +/- 
5%). The 
> > system is operating perfectly in winter but my problem is 
occuring 
> > during the summer months when attempting to get control of the 
rh. 
> > 
> > The cooling coil kicks in to drag down the temperature below the 
> > supply air temperature so as to get the humidity ratio to the 
right 
> > level, my problem is that the heating coil won't kick in to 
bring the 
> > temperature back up to the specified supply air temperature.
> > 
> > Any help would be greatly appreciated.
> > 
> > Regards,
> > John McCarthy.
> > 
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@g...





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/