The "Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve" 
goes negative below PLR=0.5.  The curve object "EIRCORPLR Air Cooled" needs 
different coefficients.

The chiller model should not have accepted these inputs, and a change request 
will be made to protect against this.

Mike



On 23 Sep 2005, at 9:58, wing sun lee wrote:

> Hi,
> 
> I want to know why there are negative values(e.g. Chiller Electric Power
> [W](Hourly)) in main result file.
> 
> 
> http://groups.yahoo.com/group/EnergyPlus_Support/files/Problem_Submittals/Harbou
> r Building/HB 050902.zip 
> 
> 
> 
> Regards,
> 
> 
> 
> SAMLEE
> 
> 
> 
> 
> 
> 
> 
> _______________________________________
>  ·Q§Y®É¦¬¨ì·s email ³qª¾¡H
>  ¤U¸ü Yahoo! Messenger http://messenger.yahoo.com.hk 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Most low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/