Dear Crawley,
That is really a good way. But in this csv file, I can only change
hourly temperature data. How about changes in each timestep,say,10
minute ?
Do data within a timestep come from interpolation?
Acatually I wanna let the building load constant all the day. Now I
see it impossible because of too many kind of data needed to change.
Thank you
John
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Drury.Crawley@e... wrote:
>
> Convert your EPW to a CSV (E+ format) using the WeatherConverter.
> Modify the temperatures there (CSV), then convert back to EPW.
>
>
>
>
> "deserteagle_zhou"
> <yp5166@1...> To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
> Sent by:
cc:
> EnergyPlus_Support@yaho Subject:
[EnergyPlus_Support] outside air temerature
>
ogroups.com
>
>
> 09/28/2005 10:15
AM
> Please respond
to
>
EnergyPlus_Support
>
>
>
>
>
>
> Hi,everybody,
>
> Is there a way to make the outdoor temperature as a constant value
in a
> E+ whole-day run? I opened the epw file, and it seemed not
possible to
> acheieve manually.
>
> Thank you!
> John
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press
> the "search" button.
>
>
>
>
>
SPONSORED LINKS
>
> Cad software Maintenance program Email software
> program software program
>
> Backup software Medical software program Wedding program
> program software
>
>
>
> YAHOO! GROUPS LINKS
>
> Visit your group "EnergyPlus_Support" on the web.
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of
Service.
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/