Re: [EnergyPlus_Support] Re: outside air temperature
John,
You could create a weather file with timestep data--starting
with a CSV--but EnergyPlus interpolates between the hourly
data automatically. So that if two hours have the same temperature,
the intermediate timesteps would as well. The easiest way
would be to take the one line (hour) of data that you want to
set as your condition the entire year and duplicate that 8759
times. If you only copied the data to the right of the
month/day/hour/minute
fields, it should be OK.
But has Linda Lawrie noted, you can also use the design days
to do that--the Winter design days do just that.
Set maximum temperature to whatever, and daily range to 0.
Search for Design Days in the documentation.
Dru Crawley
"deserteagle_zhou"
<yp5166@xxxxxxx> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent by: cc:
EnergyPlus_Support@yaho Subject: [EnergyPlus_Support] Re: outside air temerature
ogroups.com
09/29/2005 09:23 AM
Please respond to
EnergyPlus_Support
Dear Crawley,
That is really a good way. But in this csv file, I can only change
hourly temperature data. How about changes in each timestep,say,10
minute ?
Do data within a timestep come from interpolation?
Acatually I wanna let the building load constant all the day. Now I
see it impossible because of too many kind of data needed to change.
Thank you
John
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Drury.Crawley@e... wrote:
>
> Convert your EPW to a CSV (E+ format) using the WeatherConverter.
> Modify the temperatures there (CSV), then convert back to EPW.
>
>
>
>
> "deserteagle_zhou"
> <yp5166@1...> To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
> Sent by:
cc:
> EnergyPlus_Support@yaho Subject:
[EnergyPlus_Support] outside air temerature
>
ogroups.com
>
>
> 09/28/2005 10:15
AM
> Please respond
to
>
EnergyPlus_Support
>
>
>
>
>
>
> Hi,everybody,
>
> Is there a way to make the outdoor temperature as a constant value
in a
> E+ whole-day run? I opened the epw file, and it seemed not
possible to
> acheieve manually.
>
> Thank you!
> John
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press
> the "search" button.
>
>
>
>
>
SPONSORED LINKS
>
> Cad software Maintenance program Email software
> program software program
>
> Backup software Medical software program Wedding program
> program software
>
>
>
> YAHOO! GROUPS LINKS
>
> Visit your group "EnergyPlus_Support" on the web.
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of
Service.
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
the "search" button.
YAHOO! GROUPS LINKS
Visit your group "EnergyPlus_Support" on the web.
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
------------------------ Yahoo! Groups Sponsor --------------------~-->
Most low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/