Changing the supply air temperature for purchased air does not change the load.
Changing the thermostat setpoint would change the load. The thermostat
determines the amount of heating/cooling required for the zone. The supply air
temperature will change the calculated flow rate for the purchased air unit,
but it will not change the energy delivered. To see the impact of your
changes, add REPORT VARIABLE "System Node MassFlowRate" for the zone inlet
node, and you should see the flow rates change when the supply air temperature
is changed.
Mike
On 7 Oct 2005, at 6:47, kir kumar wrote:
> Dear all,
> I have simulated purchased air.idf input file changing the HEATING SUPPLY AIR
> TEMPERATURE from 50C to 70C and COOLING SUPPLY AIR TEMPERATURE from 13C to 1C
> (That means I have increased the load).Also I made the following changes HEATING
> LIMIT------ LIMIT MAXIMUM HEATING FLOW RATE(m^3/s)---- 1 COOLING LIMIT------
> LIMIT MAXIMUM COOLING FLOW RATE(m^3/s)---- 1
>
> I campared the results of changed purchased air.idf in the aforementioned way to
> the results of purchased air.idf input file(without changes). But I found no
> changes in output. Please explain me why is it so?
>
> kiran
>
>
>
> ---------------------------------
> Yahoo! India Matrimony: Find your partner now.
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/