In the BldgProps object, "ConvTol: Convergence Tolerance" (the last field) is
defined in the Auxiliary Programs doc as "specifies the convergence tolerance
used to control the iteration. When the temperature change of all nodes is less
than the convergence value, iteration ceases." Also, in the BldgProps object,
the first field "Number of years to iterate" limits the number of years the
Slab program repeats. To achieve convergence, you can increase the tolerance
(not recommended) or increase the number of years. You can set the number of
years to a large number, becuase it will stop when convergence is reached, and
then you can check the output to see how many years were simulated.
Is a nonconverged answer incorrect? In most cases it is incorrect, but that
depends on what you seek to model. When a new building is built in a site that
was previously open land, it takes a number of years for the soil to "warm up"
to a periodic steady-state. For the EnergyPlus simulation, a nonconverged
solution will produce heat flows to the ground that represent the warmup period
for the new construction. This may be of interest to some modelers. However,
most users want a converged periodic steady-state result.
Mike
On 27 Oct 2005, at 3:01, wnstot wrote:
> Mike:
> Thank you very much!
> I calculated the ground temperater with the "Slab.exe", but at the last
> line of the outputfile (*.gtp) there are the following words:
> "Convergence has NOT been gained."
> Does this mean my calcution is wrong? Or how to correct it?
>
> Could you give me a help? Thanks!
>
> Lei
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/