[EnergyPlus_Support] Inlet parameters for plant demand side splitter are not physically possible
Hi,all
There is a serve and some warnings that i can't fix.As follows:
** Severe ** Inlet parameters for plant demand side splitter
are not physically possible
** ~~~ ** Problem in input for plant demand side CHILLED WATER
LOOP
** ~~~ ** The maximum flow out of the splitter is less than
the minimum inlet flow
** ~~~ ** Flow rate inputs for the loop do not match flow
requirements of the various branches/components
** ~~~ ** Check your flow rates and make sure that flow
balances between the splitter inlet and outlets
** Warning ** SizeWaterCoil: Coil="1F_9_FPIU_CW_COIL", Cooling
Coil has leaving humidity ratio > entering humidity ratio.
** ~~~ ** ..will be sized for 50% of design entering humidity
ratio.
** Warning ** For COIL:Water:Cooling 1F_9_FPIU_CW_COIL
** ~~~ ** CalcCoilUAbyEffectNTU:Given Q impossible for given
inlet states,Proceeding With MaxHeat Transfer
I check the splitter and find no problems.Meanwhile,flow rates are
all autosized.I don't know how to eliminate the serve.
Many zones have the warning above.I don't know what do they mean.
Can anybody give me some suggestion? thanks
pch
------------------------ Yahoo! Groups Sponsor --------------------~-->
Most low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/