My apologies for the delay in finding the solution to this request. I have
found the problem. The interzone window subsurfaces are not linked to each
other. The OutsideSurfaceEnvironment Object field has been left blank:
Surface:HeatTransfer:Sub,
SubObj:0013, !- User Supplied Surface Name
WINDOW, !- Surface Type
Internal, !- Construction Name of the Surface
Obj:0004, !- Base Surface Name
, !- OutsideFaceEnvironment Object
Because this is an interzone window, it must reference another window object.
Surface:HeatTransfer:Sub,
SubObj:0013, !- User Supplied Surface Name
WINDOW, !- Surface Type
Internal, !- Construction Name of the Surface
Obj:0004, !- Base Surface Name
SubObj:0014, !- OutsideFaceEnvironment Object
And likewise SubObj:0014 must reference SubObj:0013, and so must all of the
interzone window surface pairs. I am surprised that this did not generate a
severe error. A bug report will be posted. Thank you for bringing this to our
attention.
How did I track this down? A review of the surface details report showed that
the <ExtBoundCondition> for the interior windows was ExternalEnvironment with
NoSun and NoWind. Instead, the ExtBoundCondition for SubObj:0014 should be
SubObj:0013, for example.
Mike
On 29 Sep 2005, at 22:43, Michael J. Witte wrote:
> EnergyPlus is supposed to model this type of situation. All surfaces in
> EnergyPlus have an inside temperature and an outside temperature, even if the
> construction is a single material layer. I would suggest a test replacing the
> interior window with an opaque door subsurface which has a material layer with
> the same thickness, conductivity, and density as the glass layer. Do you see
> similar surface temperatures? If you unable to resolve this, please uplaod the
> zipped idf file to the yahoo files area in the Problem Submittals folder.
>
> Mike
>
>
> On 28 Sep 2005, at 8:03, dan_grunbaum wrote:
>
> > Hi
> >
> > Just wanted to elaborate a little on my previous question.
> > I am attempting to model a commercial building which has a glazed
> > atrium surrounding it. It is intended for the office space to open to
> > the atrium or there may be a glazing layer sperating the office and
> > the atrium and therefore I need solar radiation to transmit from the
> > exterior, through the atrium and into the office space.
> >
> > If I model this with no partition seperating the atrium and office
> > space, the office space receives no solar radiation (using a solar
> > distribution of full exterior and interior). I have therefore tried
> > to model the partion with glass attached which is nearly 100%
> > transparent for all wavelengths and highly conductive. I am assuming
> > that internal windows seperating zones need to be specified twice for
> > the same reason that partitions seperating zones need to be.
> >
> > While this allows solar penetration, on a hot day the temperature of
> > the glass assigned to the partition of the atrium is a lot hoter than
> > the temperature of the corresponding glass associated with the office
> > space (41 degrees compared to 29 degrees. at this time the atrium is
> > at 47 and the office space is being conditioned to 24). As the glass
> > is theoretically one layer, I would have expected there temperatures
> > to be close or the same due to the conductivity of glass.
> >
> > This is resulting in a much lower cooling load for the office than
> > expected.
> >
> > Am I modelling this scenario wrongly or is EP unable to model it
> > correctly.
> >
> > Cheers,
> >
> > Dan
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/