Mike,if i want to supply conditioned outside air,for example,i want
to supply outside air in 14C for dehumidification in summer and
supply outside air in 18C in winter,then i have to separate the
outside air system from the fan coil system.The outside air unit
contained a OA mixer,a cooling coil,a heating coil and a supply fan.
(it seemed to the supply side of the primary air loop).But how can i
connect it to the fan coil unit?The fan coil unit is a zone equipment
but not a terminal unit.Is it possible?
pch
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
>
> 1. Both methods will introduce the same quantity of outdoor air
into the
> system. Not all fan coil system rely on a separate system to
introduce outdoor
> air, some are built with an outside air intake. Is there a big
difference
> between simulating it as a separate system or as part of the fan
coil unit?
> That depends on whether the separate system would do any special
control for
> humidity. If not, the difference in results will be small. So use
the
> simplest method unless there is a significant reason to use a more
complex
> model.
>
> 2. These values have a very small impact on coil sizing. The
default values
> can be used for most applications.
>
> 2b. Consideration of humidity control is very regional. You
should model what
> is important for your climate.
>
> Mike
>
>
> On 14 Nov 2005, at 9:39, eric_zhou1223 wrote:
>
> > Hi,
> >
> > 1.For the Dxcoil and Fancoil system, users may define required
fresh
> > air for a zone using the outdoor air mixer. The autosized value
in
> > the field ¡°maximum outside air flow rate¡± could satisfy the
> > ventilation requirement of occupants. My question is , as we
know,
> > since there exists in reality another air loop specially for the
> > fresh air inducement, is this method here only a simulative
method
> > to handle the ventilation problem? Can I use this simplified way
here
> > (defining the desired fresh air amount in above field ) to
simulate
> > a ¡° Fancoil + outdoor air¡± system, instead of using a complex
> > Fancoil system along with an additional Fresh Air Handling Unit
to
> > meet the ventilation demand? What is the difference between the
two
> > method from a fresh air supply perspective?
> >
> > 2 How can I identify the fields ¡°Zone cooling/heating design
> > supply air humidity ratio¡±? The default values can be regarded
as
> > ¡°standard ¡± values or need to be revised based on each
situation ?
> > I thought the value , specially for the heating , seem to be over
> > dry.
> >
> > Is ignoring the humidity control a common practice for an office
> > building energy simulation?
> >
> > Thank you very much
> >
> > Eric
> >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get fast access to your favorite Yahoo! Groups. Make Yahoo! your home page
http://us.click.yahoo.com/dpRU5A/wUILAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/