Re: [EnergyPlus_Support] Re: outside air problem



A separate OA system cannot feed directly to the fan coil units in EnergyPlus.  
It can only supply air directly to the zones.

Mike

On 18 Nov 2005, at 2:23, hbn_pch wrote:

> Mike,if i want to supply conditioned outside air,for example,i want 
> to supply outside air in 14C for dehumidification in summer and 
> supply outside air in 18C in winter,then i have to separate the 
> outside air system from the fan coil system.The outside air unit 
> contained a OA mixer,a cooling coil,a heating coil and a supply fan.
> (it seemed to the supply side of the primary air loop).But how can i 
> connect it to the fan coil unit?The fan coil unit is a zone equipment 
> but not a terminal unit.Is it possible?
> 
>   pch
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> <mjwitte@g...> wrote:
> >
> > 1.  Both methods will introduce the same quantity of outdoor air 
> into the 
> > system.  Not all fan coil system rely on a separate system to 
> introduce outdoor 
> > air, some are built with an outside air intake.  Is there a big 
> difference 
> > between simulating it as a separate system or as part of the fan 
> coil unit?  
> > That depends on whether the separate system would do any special 
> control for 
> > humidity.  If not, the difference in results will be small.  So use 
> the 
> > simplest method unless there is a significant reason to use a more 
> complex 
> > model.
> > 
> > 2.  These values have a very small impact on coil sizing.  The 
> default values 
> > can be used for most applications.
> > 
> > 2b.  Consideration of humidity control is very regional.  You 
> should model what 
> > is important for your climate.
> > 
> > Mike
> > 
> > 
> > On 14 Nov 2005, at 9:39, eric_zhou1223 wrote:
> > 
> > > Hi,
> > > 
> > > 1.For the Dxcoil and Fancoil system, users may define required 
> fresh 
> > > air for a zone using the outdoor air mixer. The autosized value 
> in 
> > > the field ¡°maximum outside air flow rate¡± could satisfy the 
> > > ventilation requirement of occupants. My question is , as we 
> know, 
> > > since there exists in reality another air loop specially for the 
> > > fresh air inducement, is this method here only a simulative 
> method 
> > > to handle the ventilation problem? Can I use this simplified way 
> here
> > > (defining the desired fresh air amount in above field ) to 
> simulate 
> > > a ¡° Fancoil + outdoor air¡± system, instead of using a complex  
> > > Fancoil system along with an additional Fresh Air Handling Unit 
> to 
> > > meet the ventilation demand?  What is the difference between the 
> two 
> > > method from a fresh air supply perspective?
> > > 
> > > 2  How can I identify the fields ¡°Zone cooling/heating design 
> > > supply air humidity ratio¡±?  The default values can be regarded 
> as  
> > > ¡°standard ¡± values or need to be revised based on each 
> situation ? 
> > > I thought the value , specially for the heating , seem to be over 
> > > dry.
> > > 
> > > Is ignoring the humidity control a common practice for an office 
> > > building energy simulation? 
> > > 
> > > Thank you very much
> > > 
> > > Eric
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > > 
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > 
> > > Attachments are not allowed -- please post any files to the 
> appropriate folder
> > > in the Files area of the Support Web Site.
> > > 
> > > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
> and press the
> > > "search" button.
> > > 
> > > Yahoo! Groups Links
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > 
> > 
> > 
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support      
> > EnergyPlus-Support@g...
> >
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 






------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get fast access to your favorite Yahoo! Groups. Make Yahoo! your home page
http://us.click.yahoo.com/dpRU5A/wUILAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/