Sometimes this error occurs if the design cooling humidity ratio is too high in
SYSTEM SIZING or ZONE SIZING. It can also occur if there is no moisture load
in the system (no PEOPLE, no INFILTRATION, no outside air, etc.).
Mike
On 24 Nov 2005, at 1:18, dreamerfish8146 wrote:
> Hi!
>
> Thanks a lot!I gave the delta presure and I got the fan energy
> consumption.I have another problem. There are same warnings in each
> zone.
> ** Warning ** SizeWaterCoil: Coil="COIL-Z1", Cooling Coil has leaving
> humidity ratio > entering humidity ratio.
> ** ~~~ ** ..will be sized for 50% of design entering humidity
> ratio.
>
> Could you please tell me why this happened and what can I do?
>
> Thank you!
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
AIDS in India: A "lurking bomb." Click and help stop AIDS now.
http://us.click.yahoo.com/VpTY2A/lzNLAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/