Re: [EnergyPlus_Support] Error message about controllers



To be used, a controller must be reference by another object such as a 
CONTROLLER LIST.  If this is for a fancoil (FAN COIL UNIT:4 PIPE), you do not 
need a separate controller object, the controls are integrated in the FAN COIL 
UNIT:4 PIPE object.  See example file FanCoilAutoSize.idf.

Mike


On 25 Nov 2005, at 11:48, Clarice Bleil de Souza wrote:

> Hi everybody,
> 
>   I am having an warning message for one of my controllers that I cannot get rid
>   off, specially because I could not understand exactly what it means.
> 
>   I've copied the message below. As far as I understood the controller I
>   specified has not been used but the zone is reaching the setpoint I just don't
>   know if the actuator node is the inlet node of my fancoil, according to what
>   I've specified in this controller, or not. Which is important because it will
>   change the energy consumption. I had a look at the documentation and could not
>   find Orphan Objects there I tracked the node names associated with the
>   controllers thinking that maybe I did not set a connection properly but this
>   doesn't seem to be the problem. Anyway can anybody give me a light about what
>   is going on? 
> 
>   "** Warning ** The following lines are "Orphan Objects".  These objects are in
>   the idf
>    **   ~~~   **  file but are never obtained by the simulation and therefore
>    are NOT used. **   ~~~   **  See InputOutputReference document for more
>    details. *************
>    Object=CONTROLLER:SIMPLE=6TH_1H_202_401_MBEDCONTROLLER"
> 
>   Thanks a lot fro the help
> 
>   Best regards,
> 
>   Clarice
> 
> 
> ---------------------------------
>  Yahoo! Acesso Grátis: Internet rápida e grátis.
> Instale o discador agora!
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
1.2 million kids a year are victims of human trafficking. Stop slavery.
http://us.click.yahoo.com/WpTY2A/izNLAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/