Re: [EnergyPlus_Support] Questions
1. This is not available as a report variable.
2. That seems low. Check the peak PLR on the summer design day.
3. This is just an assumption to use in the sizing calculations, the system
will not necessarily control to this value, and that is OK. The values in the
ZONE SIZING, SYSTEM SIZING, and PLANT SIZING object are *only* used to compute
the autosized equipment capacities. Once the capacities are set, this
information is not used for the actual simulation.
Mike
On 29 Nov 2005, at 14:38, eric_zhou1223 wrote:
> Hi,
>
> 1. How can I report an air-cooled chiller's PLR ?
> 2. I am also doing a testing file for a water-cooled chiller. When a
> fully-autosized method is utilized, the chiller's PLR in the eio file
> denotes to be 20%~40%, even in the hottest summer day. Is that all
> right?
> 3. When I do an E+ running with temperature-only control, does this
> program excute a little humidity controling ,since I have to fill out a
> value of "Zone cooling design supply air humidity ratio" anyway? If E+
> lets the humidity control float as a result of the temprature control,
> how can this "supply air humidity ratio" be met?
>
> Thank you for the help you would give.
>
> Eric
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/u8TY5A/tzNLAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/