[EnergyPlus_Support] Boiler name longer than 40 chars cause strange results!



Linda, Mike,
I have a simple one zone model with a baseboard heater as the only 
system. The baseboard heater is served by a Boiler:simple. 
First, I run one simulation with purchased air, so I know the zone 
needs about 1000W to reach the setpoint. Then I calculated the UA 
value and flowrates for the baseboard heater manually. Using this 
values in the baseboard heater and the plant loop results in zone 
temperatures of about 7°C (no errors, no warnings except that the 
warmup did not convergence). So my first thought was, that my manually 
calculated values are wrong, so I used autosizing to verify the 
values. But the manually calculated differs only a little from that 
one from the autosizing run. So what was the problem? I created the 
model step by step once again, and now it works without any problems. 
Checking the differences I'll found that the crucial thing is the 
length of the boiler name!!!! The boiler with the name 'Plant Heating 
Baseboard-xxxxxxxxxx xxxxxx' (41 chars) give strange results, whereas 
a boiler with the name 'Plant Heating Baseboard-xxxxxxxxxx xxxxx' (40 
chars) gives the espected results!


I will upload the files with the name boilerNameProblem.zip

Christian





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/2jUsvC/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/