Michele,
The site wind conditions are used to modify the wind speed hitting the
building, but they do not change the CP values. The Plan Area Density was
originally added for use by the CpCalculation routine to calculate
automatically the CP but that routine has been deleted from COMIS quite a
few years ago. Consequently, the PAD input no has no effect on the
computations. EnergyPlus does have a limited ability to calculate CPs for
low-rise buildings based on an ASHRAE paper (choose Wind Pressure
Coefficients as SURFACE-AVERAGE CALCULATION), but that also does not modify
the CP values as a function of local wind conditions.
Joe
----- Original Message -----
From: "Linda Lawrie" <linda@xxxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Wednesday, December 21, 2005 10:59 AM
Subject: Re: [EnergyPlus_Support] Problem about CP values
Yes, upload please. We'll try to get the COMIS
expert to look at it, if warranted.
Linda
At 09:10 AM 12/21/2005, Michele Matos wrote:
>Hi Linda,
>
>I have already removed the "Report, ComisInput" statement from my input
>file, run the simulation and put the statement again, and run it again...
>The site wind conditions are updated in the .cif but the CP values did not.
>
>Any other suggestion.
>Should I upload the idf file to the group?
>
> thanks,
>
> Michele
>
>
>
>Linda Lawrie <linda@xxxxxxxxxx> escreveu:
> Did you remove the "Report, ComisInput" statement from one run to the
> next?
>
>The .cif file is only built once per run. All the inputs are
>actually passed internally and the .cif file is only a snapshot.
>
>At 04:39 PM 12/15/2005, michelematos_ecv wrote:
>
> >I have a problem about the CP values (using COMIS air flow model).
> >When I change the model plan area density and expoent of wind velocity
> >profile, on COMIS SITE WIND CONDITIONS, the CP values in the *.cif
> >file are not updated...
> >Does anyone have the same problem? or I am missing something...
>
>Linda
>
>EnergyPlus WebSite: http://www.energyplus.gov
>Owner: EnergyPlus_Support list
>Member: EnergyPlus Development Team
>
>
>
>[Non-text portions of this message have been removed]
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any
>files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open
>EPlusMainMenu.idf and press the "search" button.
>
>
>
>
>---------------------------------
> YAHOO! GROUPS LINKS
>
>
> Visit your group "EnergyPlus_Support" on the web.
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
>---------------------------------
>
>
>
>
>
>
>---------------------------------
> Yahoo! doce lar. Faça do Yahoo! sua homepage.
>
>[Non-text portions of this message have been removed]
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any
>files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open
>EPlusMainMenu.idf and press the "search" button.
>
>Yahoo! Groups Links
>
>
>
>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
the "search" button.
Yahoo! Groups Links
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/KIlPFB/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/