Re: [EnergyPlus_Support] Full Fresh Air system with heat recovery and NO heating or cooling coils in loop
You'll need to pretend that the system is a recirc system with outside
air - ie a normal
VAV system. You will need to set the minimum OA to the total flow rate.
The heat recovery
unit will be in the OA system. Probably need to set MinimumLimit to
Proportional Minimum
in the controller:outside air.
Fred Buhl
Elmer Morrissey wrote:
>Hello all,
>
>Has anyone modelled a Single Duct VAV system that takes full fresh
>air which moderates all zonal loads through a heat recovery unit
>only?
>
>I received this fatal error…
>
> ** Fatal ** ManageControllers: Invalid controller=AHU1 OA
>CONTROLLER. The only valid controller type for an Air Primary Loop
>is CONTROLLER:SIMPLE.
> ************* Fatal error -- final processing. More error
>messages may appear.
>
>I don't have a CONTROLLER:SIMPLE because my AHU does NOT contain a
>cooling coil or a heating coil. The facility's system designers
>expect the rotary wheel will moderate all sensible and latent loads
>in their entirety.
>
>Does anyone have any ideas how I could emulate such a system?
>
>Does anyone have an example file of a FULL fresh air system with NO
>recirc air?
>
>Kind regards
>
>-Elmer
>
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/