[EnergyPlus_Support] Re: Full Fresh Air system with heat recovery and NO heating or cooling coils in loop
Hi Fred,
I've set my OA controller to the following..
CONTROLLER:OUTSIDE AIR,
AHU1 OA Controller, !- Name
NO ECONOMIZER, !- EconomizerChoice
NO RETURN AIR TEMP LIMIT,!- ReturnAirTempLimit
NO RETURN AIR ENTHALPY LIMIT, !- ReturnAirEnthalpyLimit
NO LOCKOUT, !- Lockout
PROPORTIONAL MINIMUM, !- MinimumLimit
AHU1 Supply Fan Inlet Node, !- Control_Node
AHU1 OA Inlet Node, !- Actuated_Node
0.21, !- minimum outside air flow rate {m3/s}
0.21, !- maximum outside air flow rate {m3/s}
19, !- temperature limit {C}
4, !- temperature lower limit {C}
0, !- enthalpy limit {J/kg}
AHU1 MB Relief Air Outlet Node, !- Relief_Air_Outlet_Node
AHU1 Extract Fan Outlet Node; !- Return_Air_Node
Do I need an econmizer for what I am proposing to do?
What would be the correct course of action in order to remove my
error for the fatal error described below that seems to insist on a
Controller:Simple even though I do not have a heating coil or a
cooling coil? Do I need to insert a fake cooling coil with dummy
controls?
Kind regards
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, fred buhl <wfbuhl@l...>
wrote:
>
> You'll need to pretend that the system is a recirc system with
outside
> air - ie a normal
> VAV system. You will need to set the minimum OA to the total flow
rate.
> The heat recovery
> unit will be in the OA system. Probably need to set MinimumLimit
to
> Proportional Minimum
> in the controller:outside air.
>
> Fred Buhl
>
> Elmer Morrissey wrote:
>
> >Hello all,
> >
> >Has anyone modelled a Single Duct VAV system that takes full
fresh
> >air which moderates all zonal loads through a heat recovery unit
> >only?
> >
> >I received this fatal error?
> >
> > ** Fatal ** ManageControllers: Invalid controller=AHU1 OA
> >CONTROLLER. The only valid controller type for an Air Primary
Loop
> >is CONTROLLER:SIMPLE.
> > ************* Fatal error -- final processing. More error
> >messages may appear.
> >
> >I don't have a CONTROLLER:SIMPLE because my AHU does NOT contain
a
> >cooling coil or a heating coil. The facility's system designers
> >expect the rotary wheel will moderate all sensible and latent
loads
> >in their entirety.
> >
> >Does anyone have any ideas how I could emulate such a system?
> >
> >Does anyone have an example file of a FULL fresh air system with
NO
> >recirc air?
> >
> >Kind regards
> >
> >-Elmer
> >
> >
> >
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the
appropriate folder in the Files area of the Support Web Site.
> >
> >EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the "search" button.
> >
> >Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/