[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Full Fresh Air system with heat recovery and NO heating or cooling coils in loop



Hi Fred,

I've set my OA controller to the following..

CONTROLLER:OUTSIDE AIR,
    AHU1 OA Controller,      !- Name
    NO ECONOMIZER,           !- EconomizerChoice
    NO RETURN AIR TEMP LIMIT,!- ReturnAirTempLimit
    NO RETURN AIR ENTHALPY LIMIT,  !- ReturnAirEnthalpyLimit
    NO LOCKOUT,              !- Lockout
    PROPORTIONAL MINIMUM,    !- MinimumLimit
    AHU1 Supply Fan Inlet Node,  !- Control_Node
    AHU1 OA Inlet Node,      !- Actuated_Node
    0.21,                     !- minimum outside air flow rate {m3/s}
    0.21,                    !- maximum outside air flow rate {m3/s}
    19,                      !- temperature limit {C}
    4,                       !- temperature lower limit {C}
    0,                       !- enthalpy limit {J/kg}
    AHU1 MB Relief Air  Outlet Node,  !- Relief_Air_Outlet_Node
    AHU1 Extract Fan Outlet Node;  !- Return_Air_Node

Do I need an econmizer for what I am proposing to do? 

What would be the correct course of action in order to remove my 
error for the fatal error described below that seems to insist on a 
Controller:Simple even though I do not have a heating coil or a 
cooling coil? Do I need to insert a fake cooling coil with dummy 
controls?

Kind regards

-Elmer

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, fred buhl <wfbuhl@l...> 
wrote:
>
> You'll need to pretend that the system is a recirc system with 
outside 
> air - ie a normal
> VAV system. You will need to set the minimum OA to the total flow 
rate. 
> The heat recovery
> unit will be in the OA system. Probably need to set MinimumLimit 
to 
> Proportional Minimum
> in the controller:outside air.
> 
> Fred Buhl
> 
> Elmer Morrissey wrote:
> 
> >Hello all,
> >
> >Has anyone modelled a Single Duct VAV system that takes full 
fresh 
> >air which moderates all zonal loads through a heat recovery unit 
> >only?
> >
> >I received this fatal error?
> >
> >   **  Fatal  ** ManageControllers: Invalid controller=AHU1 OA 
> >CONTROLLER. The only valid controller type for an Air Primary 
Loop 
> >is CONTROLLER:SIMPLE.
> >   ************* Fatal error -- final processing.  More error 
> >messages may appear.
> >
> >I don't have a CONTROLLER:SIMPLE because my AHU does NOT contain 
a 
> >cooling coil or a heating coil. The facility's system designers 
> >expect the rotary wheel will moderate all sensible and latent 
loads 
> >in their entirety. 
> >
> >Does anyone have any ideas how I could emulate such a system?
> >
> >Does anyone have an example file of a FULL fresh air system with 
NO 
> >recirc air?
> >
> >Kind regards
> >
> >-Elmer
> >
> >
> >
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the 
appropriate folder in the Files area of the Support Web Site.
> >
> >EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
and press the "search" button.
> > 
> >Yahoo! Groups Links
> >
> >
> >
> > 
> >
> >
> >  
> >
>







The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/