Re: [EnergyPlus_Support] Problem: low temp radiant + window frame



The window heat gain/loss values seem way too high even without the frame.  
With frame, the peak "RESISTIVE ZONE:Zone Window Heat Gain[W](Hourly)" is 68kW. 
 Without the frame, it is 56kW.  With a non-radiant system (such as 
TermReheat.idf which is the same building envelope), the max window heat gain 
is 3.4 kW.  

It appears to me that the reported window heat gain/loss may be in error when 
using radiant systems.  There is already a known issue with the reporting of 
the window frame portion of the window heat gain heat loss.  The window heat 
gain/loss reported values are computed using a simplified calculation just for 
reporting purposes.  It appears that this is not matching what is actually 
happening on the zone heat balance.  If you look at the chilled water/hot water 
loads for RadLoTempHydrHeatCool vs. TermReheat, they are the same order of 
magnitude.  So this appears to be just a reporting problem, not an energy 
balance problem.  This is a new change request (CR 6897).

Mike




On 3 Feb 2006 at 13:49, Miguel Angel Pascual Buisan wrote:

> Hello,
> 
>  
> 
>  
> 
> I have noticed a problem when using ?LOW TEMP RADIANT SYSTEM:HYDRONIC? and
> ?WindowFrameAndDivider? in the windows. Under this combination, the window
> heat gain increases to impossible values.  
> 
>  
> 
> I have uploaded to the problems submittal area, the modified example:
> ?RadLoTempHydrHeatCoolepm.idf?. In this file, is quite easy to see the
> problem when switching on/off the WindowFrameAndDivider.
> 
>  
> 
> Can anybody have a look a it?
> 
>  
> 
> Thanks in advance,
> 
>  
> 
>  
> 
> Miguel Ángel Pascual
> 
> Director Técnico
> 
>  
> 
> MIYABI       espacios urbanos bioclimáticos
> 
> Leyre 11bis, 1ºC 31002 Pamplona
> 
> Tel: 948 20 36 44  Fax: 948 20 78 60
> 
> Email: mapascual@xxxxxxxxx
> 
> Web: www.miyabi.es <http://www.miyabi.es/> 
> 
>  
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/