[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Errors occurred




I added:  Report,Surfaces,DETAILS;   to your file.  That provided more
details on
the azimuth, tilt, etc. in the EIO file.  This helped me find the problems.

1.  The Porta Frente (Metal) and Porta Fundos(Metal) are too large.  The
wall that
they are in must completely surround them--so you can't have their lower Z
coordinate
at 0 but you can have it at 0.001.

2.  In the EIO report, PAREDE DOS FUNDOS has an azimuth of 65 while PORTA
FUNDOS (VIDRO) and PORTA FUNDOS(METAL) have azimuths of 245 (facing the
other way).

3. Then I looked at your geometry--it says clockwise but most of the
vertices are entered
counterclockwise.  When I changed that, the errors go away (except for the
no. 2 above,
facing the wrong way).

4. This then gives errors on your floor and roof (these vertices must be
entered
clockwise).




                                                                                                           
                      "Milton Serpa Menezes"                                                               
                      <m.s.menezes@xxxxxxxxx.      To: EnergyPlus_Support@xxxxxxxxxxxxxxx                  
                      br>                          cc:                                                     
                      Sent by:                     Subject:  Re: [EnergyPlus_Support] Errors occurred      
                      EnergyPlus_Support@yaho                                                              
                      ogroups.com                                                                          
                                                                                                           
                                                    |--------------------------|                           
                      02/22/2006 11:18 AM           | ( ) Federal Record       |                           
                      Please respond to             | (*) Not a Federal Record |                           
                      EnergyPlus_Support            |--------------------------|                           
                                                                                                           
                                                                                                           
                                                                                                           



                                     User Filed as: Not Categorized in ERMS

        ------------------------------------------------------------------------------------|
       |                                                                                    |
       | If this external e-mail is a record and you are the first EERE recipient, click the|
       |           'File to ERMS' button in the toolbar to categorize this e-mail           |
        ------------------------------------------------------------------------------------|








Follows the idf file.

  ----- Original Message -----
  From: Drury.Crawley@xxxxxxxxxx
  To: EnergyPlus_Support@xxxxxxxxxxxxxxx
  Sent: Wednesday, February 22, 2006 10:46 AM
  Subject: Re: [EnergyPlus_Support] Errors occurred



  This means that your subsurface is not in the plane of
  the base surface.  Suggest uploading to the files
  area of the EnergyPlus_Support Yahoo Group so
  that we can look at it.




                        "Milton Serpa Menezes"

                        <m.s.menezes@xxxxxxxxx.      To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
                        br>                          cc:

                        Sent by:                     Subject:
[EnergyPlus_Support] Errors occurred
                        EnergyPlus_Support@yaho

                        ogroups.com



                        02/21/2006 09:55 PM

                        Please respond to

                        EnergyPlus_Support








  I am carrying through the thermal evaluation of a social house.  But I do
  not obtain to find what cause the error below.  Already I revised the
data
  entry, the direction of the vertex and seems to be all certainty.  Thus
  story with your aid.

  Milton


  ************* Base Surface does not surround subsurface errors
occuring...
     ************* Check that the SurfaceGeometry object is expressing the
  proper starting corner and direction [CounterClockwise/Clockwise]
     *************
     ** Warning ** Base surface does not surround subsurface (CHKSBS),
  Overlap Status=No-Overlap
     **   ~~~   **   The base surround errors occurred 3 times.
     **   ~~~   ** Surface "PAREDE FRENTE" misses SubSurface "JANELA 1"
     **   ~~~   ** Surface "PAREDE FRENTE" misses SubSurface "PORTA FRENTE
  (VIDRO)"
     **   ~~~   ** Surface "PAREDE FRENTE" misses SubSurface "PORTA FRENTE
  (METAL)"
     ** Warning ** Base surface does not surround subsurface (CHKSBS),
  Overlap Status=No-Overlap
     **   ~~~   **   The base surround errors occurred 4 times.
     **   ~~~   ** Surface "PAREDE DOS FUNDOS" misses SubSurface "JANELA 3"
     **   ~~~   ** Surface "PAREDE DOS FUNDOS" misses SubSurface "JANELA 4"
     **   ~~~   ** Surface "PAREDE DOS FUNDOS" misses SubSurface "PORTA
  FUNDOS (VIDRO)"
     **   ~~~   ** Surface "PAREDE DOS FUNDOS" misses SubSurface "PORTA
  FUNDOS(METAL)"

  [Non-text portions of this message have been removed]






  The primary EnergyPlus web site is found at:
  http://www.energyplus.gov

  The group web site is:
  http://groups.yahoo.com/group/EnergyPlus_Support/

  Attachments are not allowed -- please post any files to the appropriate
  folder in the Files area of the Support Web Site.

  EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press
  the "search" button.




                                                              SPONSORED
LINKS

  Cad software program Medical software        Backup software
                        program                 program

  Email software       Anti virus software
  program              program



                              YAHOO! GROUPS LINKS

         Visit your group "EnergyPlus_Support" on the web.

         To unsubscribe from this group, send an email to:
         EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

         Your use of Yahoo! Groups is subject to the Yahoo! Terms of
Service.









  The primary EnergyPlus web site is found at:
  http://www.energyplus.gov

  The group web site is:
  http://groups.yahoo.com/group/EnergyPlus_Support/

  Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.

  EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press
the "search" button.




  SPONSORED LINKS Cad software program  Medical software program  Backup
software program
        Email software program  Anti virus software program


------------------------------------------------------------------------------

  YAHOO! GROUPS LINKS

    a..  Visit your group "EnergyPlus_Support" on the web.

    b..  To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

    c..  Your use of Yahoo! Groups is subject to the Yahoo! Terms of
Service.


------------------------------------------------------------------------------




[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press
the "search" button.




                                                            SPONSORED LINKS
                                                                   
 Medical software      Email software program  Cad software        
 program                                       program             
                                                                   
 Backup software       Anti virus software                         
 program               program                                     
                                                                   


                            YAHOO! GROUPS LINKS

       Visit your group "EnergyPlus_Support" on the web.

       To unsubscribe from this group, send an email to:
       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

       Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.









The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/