Re: [EnergyPlus_Support] COMIS + nodes
The nodes used in the HVAC system inputs are not the same nodes used in the
COMIS simulation. "Air Flow from FromZone to ToZone through COMIS Link" (and
the reverse "Air Flow from ToZone to FromZone through COMIS Link") are what you
want to report. Note that large openings can have bidirectional flow (for
example, air can flow out the top of a large open window and flow in the
bottom) so you need to report both directions.
Mike
On 20 Feb 2006 at 20:24, sebastian.coene wrote:
> hi,
>
> My question:
>
> I have a 1 zone model and use comis for natural ventilation. Now, i
> want to know mass flow through two openings on oppostite sides of the
> zone.
> I must define 2 external nodes at each of the two windows through wich
> the air flows.
>
> BUT can i define a node in the middle of the zone for use only in
> COMIS? I can't find it in the manual? Only thing i can find is the
> defining of nodes for all types of mechanical ventilation.
> Or do i use 'Air mass flow from fromzone to tozone' for this?
>
> Any one knows the answer? Or how to define internal nodes for use in
> COMIS?
>
> Thanks in advance,
> Sebastian
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links