Re: [EnergyPlus_Support] by pass
Bypass pipes should not be necessary if the pump is intermittent, but it never
hurts to have one even if it is never used.
I am puzzled that you say for "each purchased chilled water & purchased
hotwater". You only need one purchased chilled water and one purchased hot
water to suppply the entire building. One hot water loop supplying all hot
water coils with a single purchased hot water supply object. Likewise for the
chilled water side. For an example, see the hot water loop in TermReheat.idf
Mike
On 24 Feb 2006 at 0:59, kir kumar wrote:
> Dear Micheal Witte,
> I have a simple question.
> I am using a huge building. Since I am just simulating only the building
> side and not a plant side, I understood that I need to use only purchased
> chilled water supply & Purchased Hotwater supply instead of chiller & boiler
> respectively. Now coming to my question.
> Do i really need to use bypass pipes for each purchased chilled water &
> purchased hotwater.
> thanks in advance
> kiran
>
>
> Linda Lawrie <linda@xxxxxxxxxx> wrote:
> Not my area of expertise....
>
> But I'd use the Compact HVAC objects for the Purchased Chiller and
> Hot Water and see what they give you?
>
> Others may also be able to answer more directly to your question.
>
> At 10:15 AM 2/23/2006, kir kumar wrote:
> > Do i really need to use bypass pipes for each purchased chilled
> > water & purchased hotwater.
> > thanks in advance
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
>
>
>
> SPONSORED LINKS
> Backup software program Cad software program Email software
> program Medical software program Anti virus software program
>
> ---------------------------------
> YAHOO! GROUPS LINKS
>
>
> Visit your group "EnergyPlus_Support" on the web.
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
> ---------------------------------
>
>
>
>
>
> ---------------------------------
> Jiyo cricket on Yahoo! India cricket
> Yahoo! Messenger Mobile Stay in touch with your buddies all the time.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/