Re: [EnergyPlus_Support] Control Node Setup
Try using the Set Point Manager:Single Zone Max Hum as the set point
manager for the cooling coil. Use a Humidistat in one zone to control
the steam humidifier at some minimum zone humidity set point and a
humidistat in the other zone to control the cooling coil to some maximum
zone humidity set point. You will also need to specify TEMPandHUMRAT as
the control variable for the CONTROLLER:SIMPLE used for the cooling
coil. You should also be using a Set Point Manager:Single Zone Min Hum
with the steam humidifier.
civilnug wrote:
> Hi All,
>
> I have a fixed flow system feeding two zones, on the air loop there's
> a cooling coil and a supply fan followed by a steam humidifier, I then
> have two separate reheat coils serving the two zones. In these zones I
> want to control both the temperature and the humidity.
>
> I have a CONTROLLER:SIMPLE for each of the coils (1 cooling, 2
> reheats) and SET POINT MANAGER:SINGLE ZONE REHEAT for the reheats and
> SET POINT MANAGER:SINGLE ZONE COOLING for the cooling coil.
>
> I'm able to get control of the RH or the temperature in the zones but
> not both at the same time.
>
> Could my control nodes be the source of the problem?
>
> Regards,
> John.
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press the "search" button.
>
>
>
>
> SPONSORED LINKS
> Backup software program
> <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Backup+software+program&w2=Maintenance+program+software&w3=Email+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=177&.sig=28qN3sGcwWF911j7OnqOxg>
> Maintenance program software
> <http://groups.yahoo.com/gads?t=ms&k=Maintenance+program+software&w1=Backup+software+program&w2=Maintenance+program+software&w3=Email+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=177&.sig=1FZNh98D0Ht8QnMNfbG3TQ>
> Email software program
> <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Backup+software+program&w2=Maintenance+program+software&w3=Email+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=177&.sig=pD1X5O_PBt00SkIKrscENA>
>
> Wedding program software
> <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Backup+software+program&w2=Maintenance+program+software&w3=Email+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=177&.sig=x6S7GFcuBa1Sq4_ZqCZ0Og>
> Cad software program
> <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Backup+software+program&w2=Maintenance+program+software&w3=Email+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=177&.sig=wjmBspWizYl54SWucSUuxg>
> Medical software program
> <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Backup+software+program&w2=Maintenance+program+software&w3=Email+software+program&w4=Wedding+program+software&w5=Cad+software+program&w6=Medical+software+program&c=6&s=177&.sig=0a7BUpUe9NvS9Yit40hqPA>
>
>
>
> ------------------------------------------------------------------------
> YAHOO! GROUPS LINKS
>
> * Visit your group "EnergyPlus_Support
> <http://groups.yahoo.com/group/EnergyPlus_Support>" on the web.
>
> * To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>
> * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> Service <http://docs.yahoo.com/info/terms/>.
>
>
> ------------------------------------------------------------------------
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/